Short circuit blows holes in pipes? #172469
12/19/07 11:47 PM
12/19/07 11:47 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
I got a call today from an excited contractor who was trying to explain something about some wires that sparked when they touched them with their aluminum ladder, and some pipes that had holes blown in them when it happened. I couldn't go there right away, I got there six hours later and here is what I found:

Stapled to the side of the residence is 30 feet of 6/2 SEU running to an outdoor AC unit. The SEU is over 50 years old, and the top layer of insulation is mostly gone, leaving the bare concentric neutral exposed. There is also a copper water pipe emerging from the ground and entering the house close to the wall with a spigot, along with a gas pipe. The plumbers had already been there, the copper pipe had been replaced. The homeowner also took me inside to the utility room and showed me the two copper flex connectors that had been on the water heater. They had pinholes in them. He said that the contractor's aluminum ladder was laying down alongside the house, right wher the cable was. When he picked it up, it made contact with the cable and the water pipe at the same time. There was a big boom and an arc, he said. The pipe blew open and a few minutes later they saw the water leaking out of the utility room from the pinholes in the flex pipes on the water heater.

No breakers tripped. The SEU is protected by an old GE 70 amp breaker, probably from the fifties.

I could not find any burn marks on the SEU. I can't see where contact could have been made with a hot conductor, they were both still insulated under the bare neutral.

Now I am thinking maybe it is a case of an open service neutral, with the neutral on the water pipe. But the plumbers didn't get shocked when they opened the pipes.

I didn't have much time, it was dark and late. So I shut the breaker to the AC off (nobody had thought to do that) and said I'd return to replace the circuit. But I am still kind of baffled as to what actually what happened.

Anyone ever seen this happen with the pipes?

Work Gear for Electricians and the Trades
Re: Short circuit blows holes in pipes? [Re: BigB] #172480
12/20/07 08:22 AM
12/20/07 08:22 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Is there possibly a short circuit in the water heater that may have energized the pipe? Heating element buried in sediment, perhaps?

Re: Short circuit blows holes in pipes? [Re: SteveFehr] #172489
12/20/07 09:54 AM
12/20/07 09:54 AM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
The water heater is gas.

Re: Short circuit blows holes in pipes? [Re: BigB] #172490
12/20/07 10:23 AM
12/20/07 10:23 AM
W
WESTUPLACE  Offline
Member
Joined: Mar 2004
Posts: 251
Kingwood, TX USA
The bare neutral in the SE is hot, shorted at one end and not grounded. It also could be a bad neutral in the service.

Re: Short circuit blows holes in pipes? [Re: WESTUPLACE] #172533
12/20/07 08:35 PM
12/20/07 08:35 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Did the ladder also touch the cabinet of the AC condenser at the same time? Maybe something inside that old condenser is not properly grounded with that [3-wire] SEU feeding it.

Last edited by KJay; 12/20/07 08:38 PM.
Re: Short circuit blows holes in pipes? [Re: KJay] #172536
12/20/07 09:00 PM
12/20/07 09:00 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 732
Tucson, AZ USA
No, the bare neutral was not shorted, I did check it to see if it was hot. Plus it runs all the way to the panel where it is grounded.

I found out today the plumbers fixed the pipes with the power shut off. Guess I'd better do an amp check on the service neutral and on the water pipe.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,452 Are you busy
187,374 Re: Forum
176,711 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.004s) Memory: 0.9776 MB (Peak: 1.1243 MB) Zlib enabled. Server Time: 2018-09-25 13:54:11 UTC