Panel as a raceway #171436
11/28/07 08:40 AM
11/28/07 08:40 AM
sudsy4  Offline OP
Joined: Apr 2002
Posts: 32
Elizabeth,PA USA
I am increasing the service at a commercial retail store from 1200amp to 3000amp. We are installing the new service equipment directly outside from the existing, some of the circuits from the existing will be fed from the new. Can I use the existing panel as a wireway to the new panel if the space in the panel permits? The two panels will be joined by 4inch nipples through the backs.

Thanks for any help


2017 / 2014 NEC & Related Books and Study Guides
Re: Panel as a raceway [Re: sudsy4] #171459
11/28/07 04:17 PM
11/28/07 04:17 PM
earlydean  Offline
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Among a great number of other things, Section 408.2 requires panelboards to also comply with Article 312.
Section 312.8 requires enclosures for OC devices to provide adequate space for conductors feeding through or tapping off by filling the wiring space at any cross section to no more than 40% fill for conductors, and the conductors, splices and taps no more than 75% of the cross sectional area of that space.

If you have the room, then the existing panel can be used to splice extensions into the new panel.

Re: Panel as a raceway [Re: earlydean] #171494
11/29/07 12:15 PM
11/29/07 12:15 PM
JValdes  Offline
Joined: Jun 2007
Posts: 301
South Carolina
Yes, again. Take out all the guts.

Re: Panel as a raceway [Re: JValdes] #171499
11/29/07 03:57 PM
11/29/07 03:57 PM
sudsy4  Offline OP
Joined: Apr 2002
Posts: 32
Elizabeth,PA USA
Thanks for the help, I was pretty sure it was OK but was unsure of the code section; 312.8 was what I needed to convince the owner.

Thanks again



2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 6
Trumpy 5
Popular Topics(Views)
244,387 Are you busy
181,498 Re: Forum
171,546 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.9584 MB (Peak: 1.0920 MB) Zlib enabled. Server Time: 2018-03-17 12:16:44 UTC