Where in the code does it say that the grounded conductor of a 2-wire circuit is counted as a current carrying conductor?

Horizontal Ad
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
Does it need to? It seems patently obvious that if you get a reading on an amp clamp, it's a current carrying conductor.

Joined: Sep 2007
Posts: 12
R
Member
Originally Posted by GTE
Where in the code does it say that the grounded conductor of a 2-wire circuit is counted as a current carrying conductor?


Is this in reference to derating for the number of conductors in a conduit? If it is see 310.15(B)4

Last edited by Raymfl; 11/19/07 10:55 PM.
Joined: May 2005
Posts: 984
Likes: 1
G
Member
If the current travels to the load on the phase wire, the only path that it can use to get back to the source is the other conductor.
QED


Ghost307
Joined: Mar 2005
Posts: 1,213
S
Member
For a 2-wire circuit, the circuit is always going to be unbalanced, and the neutral considered a current carrying conductor per 310.15(B)(4)(a).

Last edited by SteveFehr; 11/20/07 02:23 PM.
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
No "Neutral" in a 2 Wire Circuit.

Same level of Current will flow on both Conductors -
(unless something is terminated incorrectly!..) shocked

The same applies to:
  1. L-N 120 Volt 2 Wire Circuits, from a 1 Phase 3 wire source,
  2. L-N 120 Volt 2 Wire Circuits, from a 3 Phase 4 wire Wye source,
  3. L-N 120 Volt 2 Wire Circuits, from a 3 Phase 4 wire Delta source,
  4. L-N 277 Volt 2 Wire Circuits, from a 3 Phase 4 wire Wye source,
  5. L-L 208 Volt 2 Wire Circuits, from a 1 Phase 3 wire source,
  6. L-L 208 Volt 2 Wire Circuits, from a 3 Phase 3 wire source,
  7. L-L 208 Volt 2 Wire Circuits, from a 3 Phase 4 wire source,
  8. L-L 240 Volt 2 Wire Circuits, from a 1 Phase 3 wire source,
  9. L-L 240 Volt 2 Wire Circuits, from a 3 Phase 3 wire source,
  10. L-L 240 Volt 2 Wire Circuits, from a 3 Phase 4 wire Delta source,
  11. L-L 480 Volt 2 Wire Circuits, from a 3 Phase 3 wire source,
  12. L-L 480 Volt 2 Wire Circuits, from a 3 Phase 4 wire source,
  13. L-L-L 208 Volt, 240 Volt and 480 Volt 3 Wire Circuits, from a 3 Phase 3 or 4 wire source.


Just wanted to make the subject clear.

Scott

BTW, I think it's time to draw up some basic circuit schematics, to demonstrate the flows + levels on 2 wire circuits
(also point out when a Common Grounded Conductor is a "Balanced Neutral", and when it isn't).


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
366,345 Are you busy
289,334 Re: Forum
267,994 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5