ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Using THWN on automotive circuits
by BigB - 03/23/23 11:19 AM
Continuous load
by HotLine1 - 03/08/23 02:11 PM
How's all our Non-US folks doing?
by dsk - 03/08/23 11:56 AM
Old Computers?
by Bill Addiss - 03/04/23 05:06 PM
New in the Gallery:
Burger King crown sillyness
Burger King crown sillyness
by wa2ise, December 11
240/208 to a house
240/208 to a house
by wa2ise, October 9
Who's Online Now
0 members (), 128 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#170821 11/12/07 09:17 PM
Joined: Sep 2004
Posts: 91
S
Member
I received a phone call today from an HVAC contractor who was in the process of changing out the compressor in a RTU which was fed with a grounded B phase system. He wanted to know if he could install a 3phase monitor that would prevent his compressor from running on single phase if the unit lost a phase.

I have never had the "pleasure" of working on a grounded B phase system so I didnt' have an answer for him. He said he had changed this compressor out 1.5 years ago and it had already died.

So I started thinking.....would the compressor for this type of electrical system be different from one used on a modern 3phase system ? Could the grounded B phase be the cause of the compressor failing so soon if the compressor wasn't designed for use on a grounded B phase system ?


Joined: Jul 2004
Posts: 9,796
Likes: 15
G
Member
There is nothing special about corner delta that you wouldn't have in red leg delta. Anything that works on centertapped delta should work on corner delta (except 120v loads)
He does know this is 240, not 208?


Greg Fretwell
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by sparky 134
I received a phone call today from an HVAC contractor who was in the process of changing out the compressor in a RTU which was fed with a grounded B phase system. He wanted to know if he could install a 3phase monitor that would prevent his compressor from running on single phase if the unit lost a phase.


He doesn't need a different motor (which does not exist), he needs a Phase Loss Relay added to his starter control circuit instead.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,039 Are you busy
233,457 Re: Forum
218,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5