0 members (), 622 guests, and 28 robots.
Found while on vacation at Put in Bay Ohio.
Violations:
Wet Location Art. 406.8(B) 1
Box not listed for wet location. Art. 314.15
Box not supported Art. 314.23 (A)-(H)
Not protected from physical damage. Art. 300.4 or 340.12(10)
Non metallic cable use not permitted Art. 334.12 (B) 4
Cable not supported Art. 334.30
Not sunlight resistant (UFB) Art. 340.12 (9)
Flying Splice Art. 300.12
- Aaron H.
Thank You for uploading this! I forgot another violation
Must be GFCI protected Art. 210.8(B)4
Aaron
Where's that jaw-hits-floor smiley?
Ian A.
It was found on the porch of a store and the porch's roof had been removed several years ago and to top it all off it was RAINING and wet that day I took the picture! I wish I had checked to see if it had any
juice on it.
Aaron
I still can't figure out what the wire nut is doing there.
It looks like they used what ever they had laying around.
Aaron