0 members (), 605 guests, and 9 robots.
#169373 10/03/07 10:21 AM
EMT conduits were previously ran through a Parking Garage. We are bidding on a project at the receiving end. 150HP Pump, 1200 Amp Service Fused Disconnect, RHW wire. REF: 695.6(B)3 - does this apply? This was suggested in the meeting with the GC. I usually avoid a Service disconnect and/or have routed 'outside the building', so haven't used this method. How or where do I confirm (Iknow - AHJ, getting my ducks..)that this is a "listed" electrical circuit protective system, with a minimum 1 hour rating? I've read EMT is not rated, as it is not combustible and read the RHW rating, but can't put my finger on the exactness. Any help?
Workgear for Electricians
Last Leg #169377 10/03/07 11:16 AM
I had a fire pump with conductors run about 30' into the building. We got by this by putting the raceway down in the corner between floor and wall, building a 2x8 form and pouring it solid with concrete.
gfretwell #169380 10/03/07 11:55 AM
Check out www.drakausa.com/lifeline Their RHH wire is listed for two hours in EMT.
Alan--
Alan Nadon #169385 10/03/07 02:59 PM
Just a thought...
The RHH was $$$$$$ on a job that the EC thought would solve the dilemma.
They wound up saw cutting the floor, and going under the slab
HotLine1 #169451 10/05/07 01:01 PM
I think that a fire pump must be fed with 2 hour rated conductors. In EMT there is a special conductor that can give a 2 hr rating otherwise I think you need several inches of concrete encasement or other 2 hour fire rated enclosure.
mikesh #169452 10/05/07 01:06 PM
RRH is a lot of $$$$ but it will pass the 2 hour rate in emt.
Have fun pulling it its thick . We over size the emt.
Larry
allphase #169466 10/05/07 05:55 PM
Thanks for the input... just turned in the bid. Wish I had checked 'have fun pulling it.. it's thick' first. Pipe is oversized a bit though - 3- 250's and grnd in a 3". I did up the labor a bit, not knowing.
Thanks all.