#169143 09/27/07 07:07 AM
Joined: Mar 2005
Posts: 1,213
S
Member
I'm used to seeing either Iu or In, or the two identical, but I recently came across a molded case breaker (GE D125) that had an Iu=125A and In=100A, (adjustible from 75-100A). It's not a plug, it's built into the breaker and can't be changed beyond the pot. What, exactly, does this mean? As I understand it, Iu=125A means the contacts are rated for 125A... but with a 100A trip setting, why does that matter in the least? Why would they even bother labeling it? Am I missing something here?

Joined: Oct 2000
Posts: 2,722
Broom Pusher and
Member
Could this be a 125 Amp frame, with a 100 Amp trip?

Kind of looks that way from the Spec # (GE D 125), but who knows.

Let me check the GE catalog, then reply later.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Mar 2005
Posts: 1,213
S
Member
That's my working assumption, too, Scott. I hate guessing about things like this, though.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 187
Joined: November 2005
Top Posters(30 Days)
LarryC 3
Popular Topics(Views)
291,354 Are you busy
223,842 Re: Forum
209,243 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5