SER cable in RNC for service lateral? #168630
09/10/07 10:54 PM
09/10/07 10:54 PM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
Legal?


Greg Fretwell
2017 / 2014 NEC & Related Books and Study Guides
Re: SER cable in RNC for service lateral? [Re: gfretwell] #168631
09/10/07 11:45 PM
09/10/07 11:45 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Sure ... why not? I can't imagine the code denying extra protection of the conductors.

OTOH .... as such, aren't you required to bond the raceway at both ends? If you're going to do that ... well, that implies a splice, which in turn says 'transition to pipe as wiring method.'

I'll wimp out, and say "I don't know" laugh

Re: SER cable in RNC for service lateral? [Re: renosteinke] #168634
09/11/07 02:30 AM
09/11/07 02:30 AM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
Raceways are typically plastic around here. Sch40 or 80 in the ground with sch 80 risers.

I was asked the question because someone has a 110' service lateral to put in, piped all the way and they have that much SER in the shop. Money is the main issue

I was thinking it should be OK and I can't really find a violation but 338 and 230 are pretty vague in this area.



Greg Fretwell
Re: SER cable in RNC for service lateral? [Re: gfretwell] #168637
09/11/07 10:40 AM
09/11/07 10:40 AM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Wouldn't this simply be a case of RNC in the ground being considered a wet location and SER is only rated for damp locations?


---Ed---

"But the guy at Home Depot said it would work."
Re: SER cable in RNC for service lateral? [Re: EV607797] #168640
09/11/07 11:12 AM
09/11/07 11:12 AM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
SER is wet location, this one is marked THWN conductors.


Greg Fretwell
Re: SER cable in RNC for service lateral? [Re: gfretwell] #168645
09/11/07 01:08 PM
09/11/07 01:08 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
That's a new one to me. I've only seen type XHHW conductors in SER cable, but that's irrelevant. I asked if our local inspector would allow this and he said no. His reasoning in my situation was due to the fact that the cable contained paper spacers in it. I didn't put up much of an argument, in fact THWN was a LOT easier to pull anyway.

In your case, I'd think that THWN conductors pretty much sums it up.


---Ed---

"But the guy at Home Depot said it would work."
Re: SER cable in RNC for service lateral? [Re: EV607797] #168646
09/11/07 02:12 PM
09/11/07 02:12 PM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
There is no "paper" in this cable. After all it IS a wet location wiring method.

I bounced this off the IAEI BB and they say no because U/L doesn't list SE for underground laterals, for that matter THWN is not listed that way either. USE is the only option according to IAEI if you take the White Book as gospel.

Last edited by gfretwell; 09/11/07 02:13 PM.

Greg Fretwell
Re: SER cable in RNC for service lateral? [Re: gfretwell] #168647
09/11/07 03:52 PM
09/11/07 03:52 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Yeah, that's exactly what I meant to say! wink


---Ed---

"But the guy at Home Depot said it would work."
Re: SER cable in RNC for service lateral? [Re: gfretwell] #168864
09/18/07 07:11 PM
09/18/07 07:11 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Athough PVC was discussed at the link below, the issue of a SE type cable installed underground was kicked around.



https://www.electrical-contractor.net/forums/ubbthreads.php/ubb/showflat/Number/78280/page/0/fpart/1

Re: SER cable in RNC for service lateral? [Re: Redsy] #168876
09/18/07 10:14 PM
09/18/07 10:14 PM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
OK here is the result for "this" installation. FPL and Lee County have blessed the SER and it is going in the ground tomorrow. I suppose your mileage may vary and it might even here next time. I certainly hope the same inspector (who gave the blessing) shows up for the 305.
I am planning on going by to watch and they say I may get a chance to demonstrate my skill at shooting a pipe under a sidewalk.
We did have a volunteer who was going to strip off the jacket for the bare copper we won't need but that doesn't look like it will be necessary.


Greg Fretwell
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,419 Are you busy
187,341 Re: Forum
176,681 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 16 (0.004s) Memory: 1.0268 MB (Peak: 1.2087 MB) Zlib enabled. Server Time: 2018-09-24 06:15:05 UTC