Changing a light bulb trips OTHER circuits? #168482 09/06/07 06:43 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline OP
Member
We changed a number of T12 tubes yesterday- one of which inexplicably tripped breakers on 3 different circuits, some of which are on completely different panels. The only thing these circuits have in common are that all these panels are that they're fed from the same 100kVA transformer (208Y/120V).

What could possibly have caused this? Any of you seen something like this before? Only thing I can think of is harmonics from the ballast causing just enough harmonic surge in the transformer secondary to trip already overloaded circuits. Either that, or maybe the grounds are all messed up.

Work Gear for Electricians and the Trades
Re: Changing a light bulb trips OTHER circuits? [Re: SteveFehr] #168483 09/06/07 07:46 AM
Joined: Jan 2006
Posts: 60
R
Rick Kelly Offline
Member
Was this a one time event or can this be repeated?

Strange...

Re: Changing a light bulb trips OTHER circuits? [Re: Rick Kelly] #168485 09/06/07 08:24 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline OP
Member
We stopped replacing bulbs after it tripped... I'll let you all know what happens when we replace the others. IF we replace the others. wink

Re: Changing a light bulb trips OTHER circuits? [Re: SteveFehr] #168499 09/06/07 04:42 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
Are any of the breakers that tripped GFCI's? (suspecting luminare grounding/bonding issues)

Larry

Re: Changing a light bulb trips OTHER circuits? [Re: LarryC] #168504 09/06/07 06:32 PM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline OP
Member
Nope, no GFCIs, just normal breakers. One of the electricians here had a new theory that sounds pretty likely- he thinks the bulb grounded out; that it was getting high voltage on one side through the ballast, and the other prong shorted out to ground against the side of the fixture. This would have put a fairly high voltage and current on the ground.

Re: Changing a light bulb trips OTHER circuits? [Re: SteveFehr] #168507 09/06/07 07:29 PM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
If the pins were on the same end of the lamp, under the conditions you described, I've seen many filaments burn out when a pin hits the housing. I've never heard of one tripping a breaker, much less three, in separate panels crazy

Re: Changing a light bulb trips OTHER circuits? [Re: electure] #168528 09/07/07 06:28 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Steve,
Quote
This would have put a fairly high voltage and current on the ground.

How would current on the EGC trip other breakers?


Don(resqcapt19)
Re: Changing a light bulb trips OTHER circuits? [Re: resqcapt19] #168540 09/07/07 10:17 PM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline OP
Member
This is a 3-phase 208Y/120 setup in a 12-wide trailer, derived from two transformers, each serving a portion of the building. I suspect (but haven't verified) that the neutral bar is bonded to ground in each panel, and all panels grounded to the structural steel, which would allow the fault current to pass through the other circuits in nearby panels as a voltage spike. Several of these circuits are already overloaded (12 computers on a 20A circuit+ peripherals) and wouldn't take much to trip, regardless of how the surve/spike/etc actually got to them.

If the neutrals are bonded properly at a single point, a ground fault couldn't have impacted them in this way.

Re: Changing a light bulb trips OTHER circuits? [Re: SteveFehr] #168556 09/08/07 05:26 PM
Joined: Jan 2004
Posts: 615
J
Jps1006 Offline
Member
I hate to say it Steve, but that sounds like fuzzy electrical theory to me. If the ground and neutral are bonded together (as they should be) why would it react any differently to a short to ground than current applied to the neutral under normal operating conditions?

Is it possible there was a loose neutral splice in the fixture that was jostled as the bulb was changed?

Or is it possible you're coming from some sort of a corner grounded system, whether intentionally or inadvertently?

Re: Changing a light bulb trips OTHER circuits? [Re: Jps1006] #168560 09/09/07 05:19 AM
Joined: Nov 2005
Posts: 31
J
jdo1942 Offline
Junior Member
Steve, we have had similar situation in a store. The store was t12 magnetic ballasts and various lights thru out the store were t5 electronic, undercab lights. These lights were causing other circuits to heat up and trip. We had to use a frequency meter to find them. Apparantly the harmonic goes back down the neutral and causes issues with the other circuits. We have had up 100+ cycles and this causes breaker to burn out and all sort of strange things to happen.

Joe Ogle

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,689 Are you busy
209,610 Re: Forum
196,959 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3