I've been having a bit of debate with a colleague on sub-panel grounding on buildings wired with BX/AC as it relates to NEC 250.32(B)

Typically, sub-panels are wired with a separate ground and floating neutral, but what about with systems wired with BX/AC? Can that fourth wire be eliminated in this case, since the grounding equipment conductor is the cable sheathing or conduit? Can the cable sheathing or conduit technically be classified as a "conductor" from a code standpoint?

The reason I'm asking is we got a request to add a sub-panel in a small warehouse (for 240V loads) in NYC, previously powered by only a single 20A breaker. The cable is run in 3/4" rigid (galvanized) conduit, under concrete among other things, approximately 45' from the main building, so you can see why I'd want to try and get by without that additional conductor.

My colleague says all he does is simply adds a grounding bushing at the sub, and runs the ground from the bushing to the grounding bus... and has never been tagged, nor should he be. He argues there is absolutely no reason to run a separate ground, since the wiring system designates the cable sheathing (or conduit) as the ground - unless the conduit is in bad shape in which case it should be dug up anyway.

He further argues since this is not a new service, inspectors won't require a ground to be pulled, as we would be required with new services... and not "open their eyes" on this... unless I want to break out the jackhammer. Needless to say, there will be quite a difference quoting this job with and without breaking up concrete.

What say all of you on this one?

Joe

Horizontal Ad
Joined: Jul 2004
Posts: 9,959
Likes: 34
G
Member
If this is really "rigid" (RMC) in good shape and you put bonding bushings on each end I have no problem with this being the EGC. That actually exceeds code.


Greg Fretwell
Joined: Aug 2007
Posts: 853
L
Member
-The cable is run in 3/4" rigid (galvanized) conduit, under concrete among other things, approximately 45' from the main building, so you can see why I'd want to try and get by without that additional conductor.-


Is the rigid run from panel to panel? If so good.

Or are you pulling an AC feeder thru it as a chase

Joined: Oct 2005
Posts: 100
J
JJM Offline OP
Member
Thanks for setting the record straight. I owe my colleague an apology.

I guess I was too rigid (no pun intended) in interpreting the term conductor in 250.32(B), and am sure glad we won't need to break out the jackhammers on this one. Doesn't matter if you're getting paid or not, it's never fun.

The rigid is in good shape, installed about a decade ago. The galvanized doesn't run straight to the panel - runs up to an LB, then nipplies into a J-box - so we'll just upsize the BX to the J-box and bush it... exactly as my "old timer" colleague originally suggested.

Thanks again for the always best advice.

Joe


Link Copied to Clipboard
Advertisement:-Right

* * * * * * *
Tools for Electricians
Tools for Electricians
 
* * * * * * *

2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
Popular Topics(Views)
323,566 Are you busy
247,882 Re: Forum
231,663 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5