ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Childrens safety outlets
by dsk - 06/25/22 04:07 PM
AC-DC stage Ultra-Fast charger, how it's made?
by libellis - 06/25/22 12:17 PM
Your favourite food?
by NORCAL - 06/16/22 12:06 AM
Price action trading with RENKO
by gfretwell - 06/15/22 02:08 PM
Please Help Wiring DCDC Buck Converter
by gfretwell - 06/15/22 01:58 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 23 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2005
Posts: 100
J
JJM Offline OP
Member
I've been having a bit of debate with a colleague on sub-panel grounding on buildings wired with BX/AC as it relates to NEC 250.32(B)

Typically, sub-panels are wired with a separate ground and floating neutral, but what about with systems wired with BX/AC? Can that fourth wire be eliminated in this case, since the grounding equipment conductor is the cable sheathing or conduit? Can the cable sheathing or conduit technically be classified as a "conductor" from a code standpoint?

The reason I'm asking is we got a request to add a sub-panel in a small warehouse (for 240V loads) in NYC, previously powered by only a single 20A breaker. The cable is run in 3/4" rigid (galvanized) conduit, under concrete among other things, approximately 45' from the main building, so you can see why I'd want to try and get by without that additional conductor.

My colleague says all he does is simply adds a grounding bushing at the sub, and runs the ground from the bushing to the grounding bus... and has never been tagged, nor should he be. He argues there is absolutely no reason to run a separate ground, since the wiring system designates the cable sheathing (or conduit) as the ground - unless the conduit is in bad shape in which case it should be dug up anyway.

He further argues since this is not a new service, inspectors won't require a ground to be pulled, as we would be required with new services... and not "open their eyes" on this... unless I want to break out the jackhammer. Needless to say, there will be quite a difference quoting this job with and without breaking up concrete.

What say all of you on this one?

Joe

Joined: Jul 2004
Posts: 9,696
Likes: 11
G
Member
If this is really "rigid" (RMC) in good shape and you put bonding bushings on each end I have no problem with this being the EGC. That actually exceeds code.


Greg Fretwell
Joined: Aug 2007
Posts: 853
L
Member
-The cable is run in 3/4" rigid (galvanized) conduit, under concrete among other things, approximately 45' from the main building, so you can see why I'd want to try and get by without that additional conductor.-


Is the rigid run from panel to panel? If so good.

Or are you pulling an AC feeder thru it as a chase

Joined: Oct 2005
Posts: 100
J
JJM Offline OP
Member
Thanks for setting the record straight. I owe my colleague an apology.

I guess I was too rigid (no pun intended) in interpreting the term conductor in 250.32(B), and am sure glad we won't need to break out the jackhammers on this one. Doesn't matter if you're getting paid or not, it's never fun.

The rigid is in good shape, installed about a decade ago. The galvanized doesn't run straight to the panel - runs up to an LB, then nipplies into a J-box - so we'll just upsize the BX to the J-box and bush it... exactly as my "old timer" colleague originally suggested.

Thanks again for the always best advice.

Joe


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Top Posters(30 Days)
dsk 2
dobler 2
Asset 2
Popular Topics(Views)
293,157 Are you busy
225,230 Re: Forum
210,628 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5