What are the end fittings like, or is this only a straight run?
it appears to be a fairly straight run...
Is the exposed end deburred, or is there a sharp edge that can chafe the UF?
it could be deburred, or have an actual well pipe fitting installed to make into a jb
(house end),
or have a plastic bushing placed on said wellpump fitting
(i think it'll fit..)
Lastly, since this is not RMC or IMC, 300.5 Column 2 is out. Is this buried at 12" or deeper
a good Q, the owner says a foot but....
btw, i was thinking column #4 (GFI it...)
How long of a pull? How many 90's? Will you be able to pull 14/2 uf through 3/4?
about 50' give or take, 12 or 14 should not be a problem...
Imagine what would happen if we all took the law into our own hands
you make the thread's point for me Wirenuttt, i potentially would be doing exactly that, however small the violation is.
However exacting we as contractors may be, i doubt we qualify to wear halo's , we all toss the proverbial coin...
(but you knew that....) On the other tentacle, even a small mistake could blossom into major litigation..
so~, my options appear to be.....
1~'read 'em there rights, assume said 'wiggle room' and just do it....
2~ 'write it up' on thier bill, placing any known liability for future nearsighted gardeners on the owner....
3~ walk away.
right past thier well casing , which has a pump feed via the very same 3/4" well pipe! [This message has been edited by sparky (edited 11-16-2002).]