Hi,
I have a maintenance shop we are setting up. The engineer wants to run two services to the building from a MCC. one 200A and one 60A. Is this allowed?

Thanks

Windmiller


We all live under one King
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2005
Posts: 5,480
Likes: 3
Cat Servant
Member
Those don't sound like services; it sounds like two separate circuits.

Whatever the case, they need to be treated like feeders, with their own ground wire, as well as being tied to the building ground. Neutrals and grounds are kept separate.

Joined: Nov 2000
Posts: 2,148
R
Member
Windmiller,
They are feeders and you are not permitted to run two feeders to a single building unless you have one of the conditions listed in 225.30.
Don


Don(resqcapt19)
Joined: Jan 2005
Posts: 5,480
Likes: 3
Cat Servant
Member
Good catch, Don!