Hi,
I have a maintenance shop we are setting up. The engineer wants to run two services to the building from a MCC. one 200A and one 60A. Is this allowed?

Thanks

Windmiller


We all live under one King
Horizontal Ad
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
Those don't sound like services; it sounds like two separate circuits.

Whatever the case, they need to be treated like feeders, with their own ground wire, as well as being tied to the building ground. Neutrals and grounds are kept separate.

Joined: Nov 2000
Posts: 2,148
R
Member
Windmiller,
They are feeders and you are not permitted to run two feeders to a single building unless you have one of the conditions listed in 225.30.
Don


Don(resqcapt19)
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
Good catch, Don!


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Top Posters(30 Days)
Popular Topics(Views)
340,650 Are you busy
266,019 Re: Forum
246,944 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5