Humming in Cubicle of Medium Voltage Switchgear
#166310
07/17/07 05:51 PM
|
Joined: Dec 2006
Posts: 43
OP
Junior Member
|
Hi, I have noticed a humming that recently started in a section of medium voltage switchgear. it operates at 13.8 kV.
Could this be a harmonic imbalance or loose bus bar?
Thanks for any replies.
regards
Windmiller
We all live under one King
|
|
|
Re: Humming in Cubicle of Medium Voltage Switchgear
[Re: windmiller]
#166327
07/18/07 05:59 AM
|
Joined: Sep 2005
Posts: 120
Member
|
Yes, could be either of those or you could have tracking. If you can arrange a shutdown do it as soon as possible. A visual inspection of all insulating surfaces should be done looking for signs of tracking, use a black light for the inspection that will make it easier to find any traces of nitric acid. If you cant shut down a visual inspection with a corona camera would be best.
MV/HV Testing Specialist, "BKRMAN"
|
|
|
Re: Humming in Cubicle of Medium Voltage Switchgear
[Re: windmiller]
#217356
06/24/16 06:46 AM
|
Joined: Jun 2016
Posts: 1
New Member
|
Surely, listen for popping, or cracking sounds produced by electrical discharges also humming sounds or vibration produced by quality. With lights out, look for blue or purple corona halos. Orange or red sputter arcs are created by intermittent sparking. Best way is you cannot blackout a graphic checkup with a halo.
|
|
|
Re: Humming in Cubicle of Medium Voltage Switchgear
[Re: windmiller]
#217357
06/24/16 09:37 AM
|
Joined: Mar 2004
Posts: 947
Member
|
Thermal imaging is a nice way to find problems like loose connections. The heat stays for a while after it's turned off so you have some time to look around.
|
|
|
|
|