ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Square D "All-In-One" Panelboard
by NORCAL - 11/30/21 12:48 PM
Where is Everyone?
by luckyshadow - 11/21/21 10:14 AM
It's been an interesting career
by The Watt Doctor - 11/19/21 09:56 AM
Well I am back to stay (nearly 6 years)
by The Watt Doctor - 11/19/21 09:17 AM
Motor Load Relationships Between Fans and Pumps
by The Watt Doctor - 11/18/21 09:24 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 20 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Dec 2006
Posts: 43
W
Junior Member
Hi,
I have a 480 V switch gear we are going to feed a new maint building from. We are going underground about 50 feet from the MCC to the new building. We wont need a disco for the primary of the transformer but will for the secondary right?

Thanks


We all live under one King
2017 / 2014 NEC & Related Books and Study Guides
Joined: Nov 2000
Posts: 2,148
R
Member
You will need a disconnect at the building to satisfy 225.31. Transformers do not require disconnects, but they do require over current protection per Article 450. The feeder OCPD will provide the required primary protection. Secondary protection for the transformer many not be required, but in most cases the secondary conductors require protection at or near the transformer per 240.21(C).
Don


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Admin 3
dsk 2
Popular Topics(Views)
286,325 Are you busy
218,789 Re: Forum
204,945 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5