transformer primary protection #165991 07/09/07 05:19 PM
Joined: Dec 2006
Posts: 43
W
windmiller Offline OP
Junior Member
Hi,
I have a 480 V switch gear we are going to feed a new maint building from. We are going underground about 50 feet from the MCC to the new building. We wont need a disco for the primary of the transformer but will for the secondary right?

Thanks


We all live under one King
2017 / 2014 NEC & Related Books and Study Guides
Re: transformer primary protection [Re: windmiller] #165994 07/09/07 06:19 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
You will need a disconnect at the building to satisfy 225.31. Transformers do not require disconnects, but they do require over current protection per Article 450. The feeder OCPD will provide the required primary protection. Secondary protection for the transformer many not be required, but in most cases the secondary conductors require protection at or near the transformer per 240.21(C).
Don


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
BigB 1
Popular Topics(Views)
277,658 Are you busy
211,275 Re: Forum
198,311 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3