Hi,
I have a 480 V switch gear we are going to feed a new maint building from. We are going underground about 50 feet from the MCC to the new building. We wont need a disco for the primary of the transformer but will for the secondary right?
Thanks
We all live under one King
Work Gear for Electricians and the Trades
Workgear for Electricians
You will need a disconnect at the building to satisfy 225.31. Transformers do not require disconnects, but they do require over current protection per Article 450. The feeder OCPD will provide the required primary protection. Secondary protection for the transformer many not be required, but in most cases the secondary conductors require protection at or near the transformer per 240.21(C).
Don