transformer grounding #165690
07/03/07 11:57 AM
07/03/07 11:57 AM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
a 480-120/240 50kva dry transformer, i am doing the bonding in the trans. do i ground the trans. frame with the 480 ground and remove the 120/240 strap to the frame. all raceways are pvc with on the 480 side i have 2 phases and a ground. also this trans is mounted on a portable plant with the 120/240 volt panel, the trans and panel are on the same steel frame. what is the proper grounding and bonding.

2017 / 2014 NEC & Related Books and Study Guides
Re: transformer grounding [Re: lite bulb] #165701
07/03/07 03:36 PM
07/03/07 03:36 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Leave the strap to the frame in place.

Bond the green wire from the 480 volt side and the green wire on the 120/240 side and the building steel and any metal water pipes in the vicinity served by the secondary to the enclosure. the strap will connect the equipment grounding system to the neutral connection of the transformer.

The objective here is to clear any ground faults by ensuring a low impedance path back through the equipment ground to the neutral connection at the transformer.

On the 480 volt side, the equipment grounding conductor needs to also be connected to the enclosure to create a low impedance path back to the 480 volt distribution center, then to the service and back to the utility transformer to clear any faults to the transformer enclosure.

We cannot clear any ground faults without a complete low impedance path through the equipment grounding system.


Earl
Re: transformer grounding [Re: earlydean] #165713
07/03/07 08:13 PM
07/03/07 08:13 PM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
thanks for the help

Re: transformer grounding [Re: lite bulb] #165714
07/03/07 11:02 PM
07/03/07 11:02 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Make sure that the neutral on the secondary side is bonded to a grounding electrode system and to the EGCs for the loads. Many of the bonding straps in the transformer only bond the frame of the transformer to the case. Sometimes they bond the secondary neutral, but that is somewhat rare nowdays.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,837 Are you busy
184,197 Re: Forum
173,440 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.005s) Memory: 0.9593 MB (Peak: 1.0929 MB) Zlib enabled. Server Time: 2018-05-20 11:40:32 UTC