Is there a code article addressing abandoned wiring or disconnected cables? Seams to me I remember one saying abandoned wiring is to be removed, but I can’t find it now. Can anyone help?
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
What type of wiring or cables are you asking about? There are codes about removing abandoned cables, but that depends on the type and usage.
|
|
|
|
Joined: Jul 2004
Posts: 9,822 Likes: 20
Member
|
There are several places in the code that talk about removing accessible abandoned wiring. Other than under floor raceways they mostly refer to low voltage, computer and audio cables. You usually get away with leaving them if you tape them back and label them "spare" or words to that effect.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,349 Likes: 7
Member
|
Basic wording is 'tag at both ends'. It's within most if not all of the LV sections, Phone/data/alarm, etc.
Greg's 'spare' could be debated....both ends should match; ie; apare #1, etc. IF you want to be nit picky.
Basically, cleaning up LV can generate some extra $$ for EC's doing renovation (comm)
When drop ceilings are removed, there's what I call "sins of the past". Unsupported, fished, etc. LV cabling, and the occasional power wiring that more than likely was 'added' after the ceiling inspection(s)
We (NJ) enforce removals (LV), and whatever 'remains' has to be properly supported and identified. "Power wiring' is usually all removed, or re-installed.
Now, before the bullets start flying....I'm talking Comm/Ind work, ceiling areas, not resi.
John
John
|
|
|
|
Joined: May 2002
Posts: 6
OP
Junior Member
|
I am talking about power cables, not LV. We do both commercial and residential remodel jobs. The last commercial job we did there was pipe and mc and a ceiling full of both disconnected and live circuits. We were told to just leave it up there.
We are getting ready to do a residential remodel job and I told the owner I am going to remove all the old disconnected MN-B I can get my hands on. (He can have it and take it to the recycle center.) I just don’t like the idea of leaving all that old cable in the walls if I can easily rip it out.
Can you all reference the code articles on the subject?
|
|
|
|
Joined: Apr 2002
Posts: 7,349 Likes: 7
Member
|
OK, now for some commentary... In the NEC, references to abandonded wiring is within the LV Articles. (Period) There is no direct references to voltages, nor to wiring methods utilized within Article 300 wiring methods. Hence, we as EC's and AHJ's have to employ some common sense, which is also not referenced within the NEC.
Intent of removal is to reduce fuels in the event of a fire. Now, think about accidental powering of 'abandoned' conductors...possibly causing arcing, etc.
Additionally, there's the issue of having to work around all the 'junk' while doing you job. Also, explaining the stuff to the AHJ.
Owners that I have worked for as an EC have taken the position of complete removals, unless it is being reconnected. ALL LV is stripped out end to end.
John
John
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
Most of the Owners that I've run into want it all left "because it's cheaper and still meets the Code". I aks them if they have an issue if anything gets ripped out for free. Once they say that they don't care, the door's open for either creating a clear workspace or working around it...whichever way is easier for the Trades.
Ghost307
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
We don't have any electrical code rules in Canada but the fire protection act does. If the local jurisdiction uses the national fire code then abandoned wiring must be removed. Our local jurisdiction does not enforce it or the National fire code is not enacted here.
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
The whole purpose for the removal of LV cables is to reduce the fuel load in return air spaces. If your wiring is in conduit, it will not contribute to the fire or smoke.
Earl
|
|
|
|
Joined: Jul 2004
Posts: 9,822 Likes: 20
Member
|
From a practical sense, the reason you want to remove unused cables is the hair ball you end up with if you don't. My wife's community is fixin to pay me $300 to remove all the unused computer cables from their server rooms and relabel the stuff that stays. If they had removed the stuff as they went along they wouldn't be in this pickle. I have seen so many old cables under a computer room floor it was blocking the air flow.
Greg Fretwell
|
|
|