Since most jurisdictions in BC accept FT4 in plenums now, is it okay to run unskinned TECK and ACWU in a plenum ceiling, or am I missing some other rule here? thanks.

Tools for Electricians:
Re: FT4 [Re: jay8] #164570 06/06/07 11:49 AM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
Since teck finally has FT-4 marking on it you can run it with the sheath in tact in Greater Victoria both jurisdictions. Vancouver may not permit it as I think they still require FT-6 in plenums.
There are now some fire stop products that eliminate the requirement to strip the jacket when penetrating a fire seperation but be sure the building inspector recognizes the product and its application first.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,729 Are you busy
209,645 Re: Forum
196,989 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3