06/05/07 10:04 PM
06/05/07 10:04 PM
J
jay8  Offline OP
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
Since most jurisdictions in BC accept FT4 in plenums now, is it okay to run unskinned TECK and ACWU in a plenum ceiling, or am I missing some other rule here? thanks.

Tools for Electricians:
Re: FT4 [Re: jay8] #164570
06/06/07 12:49 PM
06/06/07 12:49 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Since teck finally has FT-4 marking on it you can run it with the sheath in tact in Greater Victoria both jurisdictions. Vancouver may not permit it as I think they still require FT-6 in plenums.
There are now some fire stop products that eliminate the requirement to strip the jacket when penetrating a fire seperation but be sure the building inspector recognizes the product and its application first.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,548 Are you busy
186,243 Re: Forum
175,723 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.9416 MB (Peak: 1.0597 MB) Zlib enabled. Server Time: 2018-08-16 08:09:35 UTC