#163572 - 05/10/07 08:55 PM Spa questions.  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Help clear this up for me. These questions are in general about a outdoor spa for a single family dwelling.

Article numbers if you could...

1. Conductors after the disconnect are required to be copper? (I have always did this, thought I read it in the past but now I can't find it.)

2. Spa/pool motors that are hardwired are NOT required to be GFCI protected?

3. If #2 is correct, why do I think I a need GFCI disconnect for a spa? (I can come up with reasons if the spa power feeds lights etc., but I have seen spas that at the disconnect have a #10 wire for the motor, and then #12 for the lgts. So sense the #10 is basically hardwired to the motor, it doesn't need to be GFCI protected?)

Thanks.



Shake n Bake

2017 / 2014 NEC & Related Books and Study Guides

#163574 - 05/10/07 09:39 PM Re: Spa questions. [Re: Trick440]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
#1 is driven by 680.21(A) "Any wiring method employed shall contain a copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG."
I suppose you could use aluminum for the current carrying conductors but you still may have a 110.3(B) problem since most skid packs say "copper only" somewhere in the instructions or labels.

#2 gets covered by 680.44 and it just says "outlets" <shall have GFCI> not "receptacles". The exceptions are
(A) self-contained unit or listed packaged equipment assembly that includes integral ground-fault circuit-interrupter
(B) A field assembled spa or hot tub rated 3 phase or rated over 250 volts or with a heater load of more than 50 amperes.
(C) Combination Pool and Spa or Hot Tub. A combination pool/hot tub or spa assembly commonly bonded.

So most spas require GFCI, cord and plug or hard wired if they don't meet A B or C above.


Greg Fretwell


Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 15 (0.002s) Memory: 0.7452 MB (Peak: 0.8619 MB) Zlib enabled. Server Time: 2017-12-12 08:28:54 UTC