ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 588 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#163306 05/05/07 11:20 PM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
went to a family members house to connect a coax cable splitter. When I started removing the connections off the old splitter there was arcing and the lites in the bsmnt. dimmed. After a few minutes they returned to normal. Could this be a result of a loose neutral or improper grounding of service. I am going to run a new ground wire to the water service and install a ground rod. Has anyone ever seen this happen before?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

sandro2 #163308 05/06/07 12:14 AM
Joined: Nov 2000
Posts: 2,148
R
Member
There is very likely a poor connection somewhere on the service neutral. The cable coax is connected in parallel with the neutral as a result of the code rules. Any arcing accompanied by lights dimming or getting brighter when disconnecting a coax is a very strong indication of a neutral problem. Note that in the case of an open neutral there is also a shock hazard...you could have 120 volts between the two parts of the cable system after you disconnect them.


Don(resqcapt19)
Joined: Apr 2004
Posts: 812
Member
I have to agree with Don, after hearing my father tell me many tales of this happening...

Ian A.


Is there anyone on board who knows how to fly a plane?

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5