#163155 - 05/02/07 05:42 PM Pole light fuses  
drillman  Offline
Member
Joined: Mar 2003
Posts: 97
Somewhere in Texas
As some of you know from chat, I had to troubleshoot a string of pole lights that tripped the breaker due to one shorted ballast. Lots of shoe leather.

I have heard some people put fuses in the pole bases. Sounds good to me. Does anyone have any suggestions as to what type/class of fuse? Fast acting or time delay? And how to size? The current set up is 480 volt 1000w HPS fixtures. They are fed by a 20 amp double pole breaker.

Also I notice that bussmann makes "breakaway" holders for pole lights, at least that what their catalog says. Not sure what "breakaway" means exactly does anyone know?

My concern is of course coordination. This will not help if the breaker trips before the fuse.


Work Gear for Electricians and the Trades

#163157 - 05/02/07 07:41 PM Re: Pole light fuses [Re: drillman]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,878
Brick, NJ USA
1k HPS ballast is 2.3 amps, & I can't remember if operating or starting current is higher.

Some locations have midget fuses in in-line fuse holders at the base; one set of poles has a fuse block (finger safe, Bussman) in the base.

My guess 3 amp, time delay.

A good place to get great info is Bussman.com; drop an e-mail to one of the fuseoligists.

John



John

#163159 - 05/02/07 07:55 PM Re: Pole light fuses [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,140
Estero,Fl,usa
I think I would start with FRN 5s. That is over double the running amps so nuisance popping shouldn't be a problem but one shorted ballast would still not overcome the breaker (16a per 20 design load)

BTW they also make indicating fuses/holders to really make troubleshooting easy.


Greg Fretwell

#163160 - 05/02/07 07:59 PM Re: Pole light fuses [Re: HotLine1]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I would guess that 'breakaway' refers to something that would unplug when the pole is knocked over.

I think the Bussman in-line fuseholders I've been using are called "HEG." They use fuses such as KTK (fast acting) and FNQ (time delay).

I strongly recommend using time-delay type fuses, especially with HID lights.

The one drawback to the fuseholders is that it is difficult to get a good crimp. If the fixtures are not already wired with stranded wire, I suggest re-wiring them - or at least make pigtails.


#163172 - 05/03/07 05:03 AM Re: Pole light fuses [Re: renosteinke]  
jdo1942  Offline
Junior Member
Joined: Nov 2005
Posts: 31
st. louis, mo. usa
Many lighting companies install inline fuses for customers as part of the service. A 1000w 480vac fixture only needs a 4 or 5 amp fuse. The installation of fuse really helps the troubleshooting, if all the lights are parallel then fuses that control each pole blows when that light has a problem.



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7704 MB (Peak: 0.9121 MB) Zlib enabled. Server Time: 2017-12-13 03:15:22 UTC