GEC and sprinkler system #163022
04/29/07 11:41 AM
04/29/07 11:41 AM
leespark  Offline OP
Joined: Jan 2004
Posts: 54
How should I handle the grounding electrode system for a 400 amp service?

I plan on installing a 1/0 copper from the main disconnect to the within 5' of where the water service enters the building and jump the water meter unspliced. I am also installing a #6 from the main disconnect to 2 ground rods spaced at least 6' apart.

However, this building has a separate incoming water service for the sprinkler system. Can I install a bonding jumper sized according to 250.66 (1/0) from the sprinkler service to the water service and connect it to the GEC using a split bolt? Or should this conductor also be run back to the main disconnect? I'm a little confused by 250.70 which I beleive is referring to my situation.


2017 / 2014 NEC & Related Books and Study Guides
Re: GEC and sprinkler system [Re: leespark] #163024
04/29/07 11:53 AM
04/29/07 11:53 AM
Alan Nadon  Offline
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
There are different ways of doing this and complying with the Code.
1. From the sprinkler system (within 5 foot of entry*) take the wire to the service.
2. From the sprinkler (within...*) take the wire to the GEC and use an irreversable crimp, not a split bolt.
3. From the sprinkler take the wire to the water pipe and use a pipe clamp.
4. If you have building steel go from the service to the steel. Then you can take the water to the steel and the sprinkler to the steel.
The last method saves alot of copper.

If it was easy, anyone could do it.


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,539 Are you busy
181,661 Re: Forum
171,710 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.9428 MB (Peak: 1.0591 MB) Zlib enabled. Server Time: 2018-03-21 16:52:00 UTC