How should I handle the grounding electrode system for a 400 amp service?

I plan on installing a 1/0 copper from the main disconnect to the within 5' of where the water service enters the building and jump the water meter unspliced. I am also installing a #6 from the main disconnect to 2 ground rods spaced at least 6' apart.

However, this building has a separate incoming water service for the sprinkler system. Can I install a bonding jumper sized according to 250.66 (1/0) from the sprinkler service to the water service and connect it to the GEC using a split bolt? Or should this conductor also be run back to the main disconnect? I'm a little confused by 250.70 which I beleive is referring to my situation.

Thanks

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Mar 2005
Posts: 399
A
Member
There are different ways of doing this and complying with the Code.
1. From the sprinkler system (within 5 foot of entry*) take the wire to the service.
2. From the sprinkler (within...*) take the wire to the GEC and use an irreversable crimp, not a split bolt.
3. From the sprinkler take the wire to the water pipe and use a pipe clamp.
4. If you have building steel go from the service to the steel. Then you can take the water to the steel and the sprinkler to the steel.
The last method saves alot of copper.
Alan--



Alan--
If it was easy, anyone could do it.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
Popular Topics(Views)
297,826 Are you busy
228,538 Re: Forum
213,370 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5