ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 4
Recent Posts
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
Bathroom electrical
by gfretwell. 08/14/17 02:05 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,887 Are you busy
175,462 Re: Forum
167,736 Need opinion
Who's Online Now
0 registered members (), 34 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#162865 - 04/26/07 12:35 PM Box mounting  
Helectric  Offline
Member
Joined: Jan 2005
Posts: 90
Brandon, SD
I'd like to mount a 4"x 12"x 16" screw cover can type box by using screws through the 4" side of the box. Does this violate any codes?


2017 / 2014 NEC & Related Books and Study Guides

#162867 - 04/26/07 02:35 PM Re: Box mounting [Re: Helectric]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,857
Brick, NJ USA
Can't put an NEC Article on that real quick....but..
Good old common sense (NOT in NEC) seems to say to ME, it's going to deflect, sag, bend, etc. Depending on where you are putting it, and what's going in/out of it.

Honestly, I would support it from the longer dimensions; strut, framing (wood) or something before the narrow dimension.

Now, IF it's in a wall cavity (2x) that may be another case, but I would support on both 4" sides.

My personal opinion, not criticism.

John


John

#162876 - 04/26/07 04:35 PM Re: Box mounting [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
I'm with John. You can use the 4" side if you use both of them. Otherwise it is just to long a "lever" on a small attaching point.


Greg Fretwell

#162885 - 04/26/07 07:20 PM Re: Box mounting [Re: Helectric]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
I can't chime in on code issues, but what is going inside the box and how is it getting there?

If it is a junction box and it is being used with solidly supported EMT or IMC, why not?

Larry C


#162889 - 04/26/07 08:50 PM Re: Box mounting [Re: LarryC]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,857
Brick, NJ USA
Larry:
12 x 16 is larger than 100 sq inches, right??
Doesn't 314.23 (E) say 'no-no'??

Helectric, what's the details??
John


John

#162903 - 04/27/07 08:52 AM Re: Box mounting [Re: HotLine1]  
ghost307  Offline
Member
Joined: May 2005
Posts: 907
Chicago Illinois USA
314.23 also says that the box is considered supported by the raceway only if there's more than 1 conduit and only if they are made up into threaded hubs on the box.
It doesn't apply to a regular sheet metal box.


Ghost307

#162905 - 04/27/07 10:00 AM Re: Box mounting [Re: ghost307]  
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
I'd have to agree with both the common sense logic as well as my interpretation of 314.23 - and say no to this arrangement.

Although there may be a particular application where this mounting wouldn't be a problem, I can't think of one off hand.


#163953 - 05/21/07 03:13 PM Re: Box mounting [Re: Zapped]  
Helectric  Offline
Member
Joined: Jan 2005
Posts: 90
Brandon, SD
Sorry it's taken me so long to get back to this. Things have been busy here.
I want to hang this box below some duct work in a pedestrian aisle at a point where there is poor visibility of approaching forklift cross traffic. I will then mount a micro-strobe and annunciator on the bottom edge and apply an adhesive label to the front and back of the box that says "Forklift approaching" The stobe and annunciator will be triggered by existing sensors to warn pedestrians of approaching forklifts (who's drivers can't see past their load)


#163959 - 05/21/07 05:18 PM Re: Box mounting [Re: Helectric]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
How about a "machine status light tower" stobe light on a piece of 1/2" IMC? No box, light weight, and simple?


#163967 - 05/21/07 09:10 PM Re: Box mounting [Re: LarryC]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Found a link to the type of lights I am talking about.

C-H stacklights

Also the pipe is 3/4" NPT.

Larry C


Page 1 of 2 1 2

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 16 (0.003s) Memory: 0.8184 MB (Peak: 0.9993 MB) Zlib enabled. Server Time: 2017-08-18 03:08:20 UTC