Box mounting #162865
04/26/07 12:35 PM
04/26/07 12:35 PM
H
Helectric  Offline OP
Member
Joined: Jan 2005
Posts: 90
Brandon, SD
I'd like to mount a 4"x 12"x 16" screw cover can type box by using screws through the 4" side of the box. Does this violate any codes?

2017 / 2014 NEC & Related Books and Study Guides
Re: Box mounting [Re: Helectric] #162867
04/26/07 02:35 PM
04/26/07 02:35 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
Can't put an NEC Article on that real quick....but..
Good old common sense (NOT in NEC) seems to say to ME, it's going to deflect, sag, bend, etc. Depending on where you are putting it, and what's going in/out of it.

Honestly, I would support it from the longer dimensions; strut, framing (wood) or something before the narrow dimension.

Now, IF it's in a wall cavity (2x) that may be another case, but I would support on both 4" sides.

My personal opinion, not criticism.

John


John
Re: Box mounting [Re: HotLine1] #162876
04/26/07 04:35 PM
04/26/07 04:35 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,290
Estero,Fl,usa
I'm with John. You can use the 4" side if you use both of them. Otherwise it is just to long a "lever" on a small attaching point.


Greg Fretwell
Re: Box mounting [Re: Helectric] #162885
04/26/07 07:20 PM
04/26/07 07:20 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
I can't chime in on code issues, but what is going inside the box and how is it getting there?

If it is a junction box and it is being used with solidly supported EMT or IMC, why not?

Larry C

Re: Box mounting [Re: LarryC] #162889
04/26/07 08:50 PM
04/26/07 08:50 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,024
Brick, NJ USA
Larry:
12 x 16 is larger than 100 sq inches, right??
Doesn't 314.23 (E) say 'no-no'??

Helectric, what's the details??
John


John
Re: Box mounting [Re: HotLine1] #162903
04/27/07 08:52 AM
04/27/07 08:52 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 951
Chicago Illinois USA
314.23 also says that the box is considered supported by the raceway only if there's more than 1 conduit and only if they are made up into threaded hubs on the box.
It doesn't apply to a regular sheet metal box.


Ghost307
Re: Box mounting [Re: ghost307] #162905
04/27/07 10:00 AM
04/27/07 10:00 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
I'd have to agree with both the common sense logic as well as my interpretation of 314.23 - and say no to this arrangement.

Although there may be a particular application where this mounting wouldn't be a problem, I can't think of one off hand.

Re: Box mounting [Re: Zapped] #163953
05/21/07 03:13 PM
05/21/07 03:13 PM
H
Helectric  Offline OP
Member
Joined: Jan 2005
Posts: 90
Brandon, SD
Sorry it's taken me so long to get back to this. Things have been busy here.
I want to hang this box below some duct work in a pedestrian aisle at a point where there is poor visibility of approaching forklift cross traffic. I will then mount a micro-strobe and annunciator on the bottom edge and apply an adhesive label to the front and back of the box that says "Forklift approaching" The stobe and annunciator will be triggered by existing sensors to warn pedestrians of approaching forklifts (who's drivers can't see past their load)

Re: Box mounting [Re: Helectric] #163959
05/21/07 05:18 PM
05/21/07 05:18 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
How about a "machine status light tower" stobe light on a piece of 1/2" IMC? No box, light weight, and simple?

Re: Box mounting [Re: LarryC] #163967
05/21/07 09:10 PM
05/21/07 09:10 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Found a link to the type of lights I am talking about.

C-H stacklights

Also the pipe is 3/4" NPT.

Larry C

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Popular Topics(Views)
249,451 Are you busy
187,369 Re: Forum
176,708 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 16 (0.009s) Memory: 1.0248 MB (Peak: 1.2054 MB) Zlib enabled. Server Time: 2018-09-25 11:07:42 UTC