Fire Alarm T Tap #161678 04/06/07 02:18 PM
Joined: Feb 2004
Posts: 74
C
CRM Offline OP
Member
I've got an edwards QS4 fire alarm, I've got an adressible loop going around the building, 2 wires leaving and 2 wires returning. Can I tap 2 wires off the loop at any point to feed an adressible pull station, but not run 2 wires back onto the loop. Thanks for any input.

Work Gear for Electricians and the Trades
Re: Fire Alarm T Tap [Re: CRM] #161710 04/06/07 09:21 PM
Joined: Aug 2001
Posts: 329
S
Steve Miller Offline
Member
The 2 back are what create the Class A system. To the best of my knowledge, no you can't. You need the 2 going back. If the 2 going out get broken the Class A will still function because it is "double end fed".

Re: Fire Alarm T Tap [Re: Steve Miller] #161734 04/07/07 07:46 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Depending on how far you need the circuit extension, and the size room the device is in, the NFPA 72 (FA Code) would allow you to take two cables (2 wires in each plus shield) and run to the new device. This would effectively give you the two there and the two back.

You have some limitations in this scheme if they are in the same raceway or bundle because there would need to be some separation if the area served was large.


Ron
Re: Fire Alarm T Tap [Re: Ron] #161738 04/07/07 08:38 AM
Joined: Jul 2001
Posts: 311
F
Frank Cinker Offline
Member
I have limited knowledge of addressable fire alarm systems. My question is aren't two wire class B system initiating device circuits more popular than the class A system? What are the advantages of the class A system?

Last edited by Frank Cinker; 04/07/07 08:41 AM. Reason: typo
Re: Fire Alarm T Tap [Re: Frank Cinker] #161742 04/07/07 10:00 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Class A is generally not code required, but offers better reliability during certain faults and open circuit conditions.


Ron
Re: Fire Alarm T Tap [Re: Ron] #161744 04/07/07 10:38 AM
Joined: Sep 2006
Posts: 58
Y
yanici Offline
Member
Why not just identify your"in" and "out" pairs and then run 2 pair to the new pull station. Then splice them accordingly at the junction.

Re: Fire Alarm T Tap [Re: yanici] #161748 04/07/07 11:10 AM
Joined: Mar 2005
Posts: 20
D
deverson Offline
Member
T-taps are allowed on Simplex addressable systems. I'm not sure if there is a maximum number of T-taps per Mapnet zone. If you remove a head or a base you do get notification of that trouble. T-tapping is a nice feature for the troubleshooter because when you have to remove a base for replacement you don't end up with up to 256 missing heads. These are initiating circuits and NOT signal circuits. I've had lots of experience on 4100, 4100U panels and on hardwired in lots of buildings, installation and repair.
Dave

Re: Fire Alarm T Tap [Re: deverson] #161830 04/08/07 04:31 AM
Joined: Jul 2005
Posts: 8
S
sparkydudeuk Offline
Junior Member
Over here in the Uk where we use addressable alarm systems, we are only permitted to take t taps off a system if it is wired in a four core and ground cable. You are not permitted to use a 2 core cable as it will not provide the recommended monitoring and re feeding of the loop if there is a fault and the isolators operate. With the systems we use, you can get an interface which you put on the loop and then wire a conventional zone with 2 cores to you r chosen area, and then it is monitored via the interface.

Nick


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,645 Are you busy
195,027 Re: Forum
184,441 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3