#161190 - 03/31/07 10:51 AM Neutral color coding # 6 and smaller  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 828
NC
Anybody know the reasoning behind the requirement that neutral conductors #6 and smaller must have a outer white or gray finish and cannot be tapped at the terminations? This is sorta aggravating when my supply house don't supply white unless you buy a whole roll, then I have to go to Lowes and pay triple price or so for it. Thanks for the input. Steve...


Work Gear for Electricians and the Trades

#161195 - 03/31/07 11:42 AM Re: Neutral color coding # 6 and smaller [Re: sparkync]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,120
Estero,Fl,usa
Wire manufacturers on the CMP?


Greg Fretwell

#161197 - 03/31/07 11:48 AM Re: Neutral color coding # 6 and smaller [Re: sparkync]  
RobbieD  Offline
Member
Joined: Feb 2003
Posts: 231
Canada
Here #2 and smaller have to be white.
I would say this requirement is out there because those sizes are manufactured white. The bigger ones are not so they allow you to colour tape them.
If people were to just use black all the time and tape it white, I bet that some might do a crappy tape job and it would fall off, some might not colour it at all, there would be confusion on what one is the identified conductor.
Your supply place is just trying to make more money by only selling by the roll.


#161370 - 04/02/07 11:25 AM Re: Neutral color coding # 6 and smaller [Re: RobbieD]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I agree that's a bit of an issue around here too. No suppliers seem to stock colors anymore. Even Home Depot only stocks black. If I am lucky, I might be able to buy some short pieces they have from when they did sell colors. Then, this might be also due to the fact that our inspectors are somewhat lax on this requirement in this area.


---Ed---

"But the guy at Home Depot said it would work."

#161414 - 04/02/07 10:04 PM Re: Neutral color coding # 6 and smaller [Re: sparkync]  
ausador  Offline
Member
Joined: Mar 2007
Posts: 49
Central Florida
Picture opening a J-box in the middle of a 200' run and seeing 11 black #12 conductors entering and exiting in 3/4" conduit. Thats why.....

Larger conductors typically are dedicated for a specific load and are not tapped in multiple J-boxes. The smaller conductors typically pass thru mulitple J-boxes and are tapped multiple times and are often re-used and reconfigured during remodel work.

How do you identify the neutral(s) if it isn't color coded in each and every pull/J-box? The sole intent of this code article as I have always understood it is to make your and mine job easier (along with the unqualified wanna-be maintenence xxxx that might electrocute themselves).

Neutrals are white for the same reason that grounds are green or bare, so that you can identify them readily at every pull box, fitting, and splice box without de-energizeing every circuit associated with them, breaking the joints/cutting them, and then ringing them out.

Come on....think about it for a minute?

Buy the roll of white wire, it isn't as if it spoils on the shelf or in your van or truck. Another job will come along soon where you can use some more of it anyway.

Last edited by iwire; 04/03/07 04:40 PM.

#161462 - 04/03/07 11:29 AM Re: Neutral color coding # 6 and smaller [Re: ausador]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I can understand your position on #14-#10, but on #8 or #6?


---Ed---

"But the guy at Home Depot said it would work."

#161495 - 04/03/07 04:30 PM Re: Neutral color coding # 6 and smaller [Re: EV607797]  
ausador  Offline
Member
Joined: Mar 2007
Posts: 49
Central Florida
Even #8 and #6 are often used for branch circuits for lighting especially in large multi-story buildings. I often have to use #6 conductors for standby lighting loads when they originate in a E-panel two floors below and the run length is over 400' in total.

Normally in small buildings I admit that this is not an issue, but in large multi-story buildings, schools, etc...etc...?

I have added standby lighting/emergency power via automatic transfer switch and a generator to many schools in alaska. In every case the lighting circuit conductors were spec'd as #8 or more often #6 conductors.

Again should I color code the conductors black,red,blue,white/brown,orange,yellow,gray or just pull six or eight black conductors?

I have never had any problem with this particular requirement because it is one that makes my job easier when it comes to troubleshooting and remodel work.


#161499 - 04/03/07 04:43 PM Re: Neutral color coding # 6 and smaller [Re: ausador]  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Here we don't use specific colors for 8 and larger.

However we do mark the conductors at any box they terminate in.









Bob Badger
Construction & Maintenance Electrician
Massachusetts

#161500 - 04/03/07 04:48 PM Re: Neutral color coding # 6 and smaller [Re: ausador]  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Originally Posted by ausador
Again should I color code the conductors black,red,blue,white/brown,orange,yellow,gray or just pull six or eight black conductors?


Well as far the ungrounded conductors you are more than free to leave them all black, all purple or a random mix.



Bob Badger
Construction & Maintenance Electrician
Massachusetts

#161501 - 04/03/07 05:12 PM Re: Neutral color coding # 6 and smaller [Re: iwire]  
ausador  Offline
Member
Joined: Mar 2007
Posts: 49
Central Florida
I could pull all black for the ungrounded conductors or purple or pink or any other color as iwire has pointed out. But why would I?, to save $375.00 on a $260,000.00 dollar job in wire cost?

I have no problem at all with buying the full reels of wire, as I said before it doesn't spoil and I will use what is left over on the next job or maybe the one after that.

Having some #8 and #6 white on the shelf and ready to use has never hurt me, so I fail to see what the problem is. (of course I also have 1/0, 2/0, 3/0 copper, about 900 assorted new and used breakers, and 200amp 30 space panels along with 125, 150 and 200 mainkits for them.)

Yes I have some wire reels that I "might" not use use again for a year or more. It is part of the cost of doing business and when I get that night call-out and I need some #6 white I will have it.




Page 1 of 2 1 2

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 16 (0.005s) Memory: 0.8213 MB (Peak: 1.0022 MB) Zlib enabled. Server Time: 2017-10-17 04:10:01 UTC