This will be the first rigid service mast job on a house. I know you have to tie the mast off to the houde. My question is how. The utility company says nothing but the guide wire to be tie to mast. I was thinking of using a clevis and 1/8 wire to a eye bolt through the roof. Does this sound right. Thanks.
|
|
|
|
Joined: Nov 2005
Posts: 31
Junior Member
|
We use a piece of 1/2" emt with the ends flattened and a minnie to attach to the mast. This is easy and you generally have the materials
|
|
|
|
Joined: Apr 2002
Posts: 7,336 Likes: 7
Member
|
PSE&G specs (NJ) are: 1/4" Galv wire and a 30 degree min. angle; "securely fastened to anchored studing". Also, RGC mast must be attached to structure (house) with 1/2" machine through bolts thru wall studs. min of 2 straps, each 1000lbs horiz pull. Minimum conduit 2" max 3".
From PSE&G Green Book, 2005 Edition. I have heard rumors that they now want 2-1/2" RGC as a min.
John
John
|
|
|
|
Joined: Jan 2003
Posts: 1,429
Member
|
"I have heard rumors that they now want 2-1/2" RGC as a min."
Just did one, and yes for PSE&G 2-1/2" Rigid.
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
right now my POCO is still using 2 inch rigid but i heard the rumors as well the cost for 2.5 rigid genrally more but i think some poco get smart with this because some area did actally used Al rigid but our speced say steel rigid Merci , Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Oct 2003
Posts: 259
Member
|
N star requires 2 1/2 ridged in MA. I did one 3 months ago.
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
PSE&G specs (NJ) are: 1/4" Galv wire and a 30 degree min. angle; "securely fastened to anchored studing". Also, RGC mast must be attached to structure (house) with 1/2" machine through bolts thru wall studs. min of 2 straps, each 1000lbs horiz pull. Minimum conduit 2" max 3".
From PSE&G Green Book, 2005 Edition. I have heard rumors that they now want 2-1/2" RGC as a min.
John John, I did a service not too long ago that the other "mechanic" claimed "didn't need no stinking guy wire." He also only used (1) 2" thinwall strap! Thinwall! Machine screw bolts? LOL! Sheetrock screws! He was a know it all so who was I to tell him otherwise? Amazingly, it passed inspection. I wired the panel and did the grounding.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
They (manufacturers like b-line ect) make a 'mast kit' if over a roof. It consists of some 1/2" or 3/4" RMC fittings and rings that go on the conduit, and some brackets to bolt to the roof. You get to thread your own RMC for it. But this is identified in the instuctions for the purpose. 230.28 Service Masts as Supports. Where a service mast is used for the support of service-drop conductors, it shall be of adequate strength or be supported by braces or guys to withstand safely the strain imposed by the service drop. Where raceway-type service masts are used, all raceway fittings shall be identified for use with service masts. Only power service-drop conductors shall be permitted to be attached to a service mast.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Mar 2004
Posts: 807
Member
|
Yes it uses 3/4" fittings and we are required to use them where I am. The Ahj said no more flattened emt allowed. So another thirty dollars for the pipe and mast kit and another forty minutes measuring, cutting and threading IMC the price of an upgrade just went up another hundred dollars.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Quick side questions here: Are these places that are requiring 2"+ RMC to be installed so 'they' (the POCO) pulls the conductors? Or are you also pulling the conductors? Do these places also have min. 200a services too?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
Posts: 46
Joined: May 2007
|
|
|
|
|