Slipping conductors #160704
03/24/07 06:53 PM
03/24/07 06:53 PM
M
myklein  Offline OP
Junior Member
Joined: Mar 2007
Posts: 2
California/Arizona
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?

Tools for Electricians:
Re: Slipping conductors [Re: myklein] #160706
03/24/07 07:37 PM
03/24/07 07:37 PM
T
tshea  Offline
Member
Joined: Nov 2003
Posts: 16
racine, wi
No code violation unless you overfill the conduit. More of a mechanical problem. Good luck!

Re: Slipping conductors [Re: myklein] #160711
03/24/07 08:02 PM
03/24/07 08:02 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
Hi there myklien,
Welcome to ECN, mate!. grin
Personally (coming from a guy in New Zealand) I'd avoid drawing cables into a conduit that carries existing cabling, for the reason that if you aren't careful you can burn the insulation off of the existing cables by friction, you can use all the lube you like, but at the end of the day, you still have to be careful.
Bends in the conduit are where the most problems arise.

Re: Slipping conductors [Re: myklein] #160771
03/25/07 05:01 PM
03/25/07 05:01 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Originally Posted by myklein
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?


No, not an NEC one.

We do it quite often but like anything some commonsense must be used. You can not expect to slide a few new conductors in a conduit that is already loaded. Or as Mike said a conduit that is full of bends.

Many times the best way is to choose one of the existing conductors and use it as a pull rope.

If I need two new conductors I will tie three onto an existing conductor and pull that one out to pull the new ones in.

Go slow, again for the reason Mike pointed out, friction could burn through a stationary conductor.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Slipping conductors [Re: iwire] #160801
03/26/07 12:27 AM
03/26/07 12:27 AM
M
myklein  Offline OP
Junior Member
Joined: Mar 2007
Posts: 2
California/Arizona
I'm a retired electrician, and have always advised against slipping wires because of the possibility of insulation burn. CalTrans California's Transportation entity has written in there standards wire is not to be slipped at any time.
I have seen it written into so many job specs that I thought it was also in the NEC.
Thank you to all that replied.

Re: Slipping conductors [Re: myklein] #160809
03/26/07 07:12 AM
03/26/07 07:12 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Armored cable (with braided wire armor) is great for this- the armor slides easily along other armored cables, and is very resistant to damage.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007