Slipping conductors
#160704
03/24/07 06:53 PM
|
Joined: Mar 2007
Posts: 2
OP
Junior Member
|
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?
|
|
|
Re: Slipping conductors
[Re: myklein]
#160706
03/24/07 07:37 PM
|
Joined: Nov 2003
Posts: 16
Member
|
No code violation unless you overfill the conduit. More of a mechanical problem. Good luck!
|
|
|
Re: Slipping conductors
[Re: myklein]
#160711
03/24/07 08:02 PM
|
Joined: Jul 2002
Posts: 8,379
Member
|
Hi there myklien, Welcome to ECN, mate!.  Personally (coming from a guy in New Zealand) I'd avoid drawing cables into a conduit that carries existing cabling, for the reason that if you aren't careful you can burn the insulation off of the existing cables by friction, you can use all the lube you like, but at the end of the day, you still have to be careful. Bends in the conduit are where the most problems arise.
|
|
|
Re: Slipping conductors
[Re: myklein]
#160771
03/25/07 05:01 PM
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit? No, not an NEC one. We do it quite often but like anything some commonsense must be used. You can not expect to slide a few new conductors in a conduit that is already loaded. Or as Mike said a conduit that is full of bends. Many times the best way is to choose one of the existing conductors and use it as a pull rope. If I need two new conductors I will tie three onto an existing conductor and pull that one out to pull the new ones in. Go slow, again for the reason Mike pointed out, friction could burn through a stationary conductor.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Re: Slipping conductors
[Re: iwire]
#160801
03/26/07 12:27 AM
|
Joined: Mar 2007
Posts: 2
OP
Junior Member
|
I'm a retired electrician, and have always advised against slipping wires because of the possibility of insulation burn. CalTrans California's Transportation entity has written in there standards wire is not to be slipped at any time. I have seen it written into so many job specs that I thought it was also in the NEC. Thank you to all that replied.
|
|
|
Re: Slipping conductors
[Re: myklein]
#160809
03/26/07 07:12 AM
|
Joined: Mar 2005
Posts: 1,213
Member
|
Armored cable (with braided wire armor) is great for this- the armor slides easily along other armored cables, and is very resistant to damage.
|
|
|
|
|