Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?

Horizontal Ad
Joined: Nov 2003
Posts: 16
T
Member
No code violation unless you overfill the conduit. More of a mechanical problem. Good luck!

Joined: Jul 2002
Posts: 8,441
Likes: 4
Member
Hi there myklien,
Welcome to ECN, mate!. grin
Personally (coming from a guy in New Zealand) I'd avoid drawing cables into a conduit that carries existing cabling, for the reason that if you aren't careful you can burn the insulation off of the existing cables by friction, you can use all the lube you like, but at the end of the day, you still have to be careful.
Bends in the conduit are where the most problems arise.

Joined: Jan 2003
Posts: 4,391
I
Moderator
Originally Posted by myklein
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?


No, not an NEC one.

We do it quite often but like anything some commonsense must be used. You can not expect to slide a few new conductors in a conduit that is already loaded. Or as Mike said a conduit that is full of bends.

Many times the best way is to choose one of the existing conductors and use it as a pull rope.

If I need two new conductors I will tie three onto an existing conductor and pull that one out to pull the new ones in.

Go slow, again for the reason Mike pointed out, friction could burn through a stationary conductor.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Mar 2007
Posts: 2
M
myklein Offline OP
Junior Member
I'm a retired electrician, and have always advised against slipping wires because of the possibility of insulation burn. CalTrans California's Transportation entity has written in there standards wire is not to be slipped at any time.
I have seen it written into so many job specs that I thought it was also in the NEC.
Thank you to all that replied.

Joined: Mar 2005
Posts: 1,213
S
Member
Armored cable (with braided wire armor) is great for this- the armor slides easily along other armored cables, and is very resistant to damage.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,413
Joined: April 2002
Top Posters(30 Days)
Popular Topics(Views)
363,451 Are you busy
286,256 Re: Forum
264,795 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5