Dryer #158779
08/23/06 08:30 PM
08/23/06 08:30 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
During a recent 4-wire Dryer install Lowe's had delivered a new dryer and asked me which cord to use, I told them 4-wire. They changed their cord. After they left I decided to check their work. They had no connector on the cord, ( they told the homeowner that they could not make it fit and really did not need it ).Also they did not remove the neutral bonding jumper. I called them and told them it was wrong. Their response was that it was a standard install and did not need a license to do this work. Am I wrong thinking that this work was ok?.

Business, Office, Estimating, Legal:
Re: Dryer #158780
08/23/06 09:03 PM
08/23/06 09:03 PM
K
kencr  Offline
Member
Joined: Jul 2004
Posts: 35
Southern, NJ USA
Your not wrong at all... maybe the local inspector should get a call and be told .. its crazy that thet could leave it like that.. But I am sure it is done many times everyday around the country..

Makes you wonder ??

Re: Dryer #158781
08/24/06 03:58 PM
08/24/06 03:58 PM
S
Sparks30  Offline OP
Member
Joined: Mar 2002
Posts: 125
Connecticut.usa
I e-mail the state electrical inspector. This is reponse. ( you really need to contact Richard at the Department of Consumer Protection with questions regarding licensing.) This is what I sent them. (Hello,
My name is Sam and I have a small question. I am an E-1. During a recent 4-wire Dryer install Lowe's had delivered a new dryer and asked me which cord to use, I told them 4-wire. They changed their cord. After they left I decided to check their work. They had no connector on the cord, ( they told the homeowner that they could not make it fit and really did not need it ).Also they did not remove the neutral bonding jumper. I called them and told them it was wrong. Their response was that it was a standard install and did not need a license to do this work. Am I wrong thinking that this work was ok?. Thank you for your time. Sam) Nice reponse!


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 95
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,007 Are you busy
181,001 Re: Forum
171,245 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.9506 MB (Peak: 1.0704 MB) Zlib enabled. Server Time: 2018-02-18 05:06:54 UTC