Bonding screw #155573
01/17/05 10:27 AM
01/17/05 10:27 AM
R
rusty  Offline OP
Junior Member
Joined: Dec 2002
Posts: 6
aurora, ne. usa
I just wondered if anyone wanted to speculate on something I saw the other day.

In a new steel storage building, a 200A Sq D panel was being fed directly from the meter. A grounding kit was installed in the panel. The GEC and bonding jumper to the steel building were the only wires on the grounding bar, and any neutrals were on the other (neutral bar). Conduit was run for all circuits with no EG. What caught my attention was arcing (just the marks) around the bonding screw. I checked the screw to see if it was tight, and turned it about 3 full turns.

I'm just wondering what caused this arcing. Did something short out to the conduit and return to the panel and arc between the screw and bar? I think I can imagine how this would happen, but would like to hear some ideas.

Thanks for all your help in the forum. I rarily post, but lurk everyday.

Business, Office, Estimating, Legal:
Re: Bonding screw #155574
01/17/05 10:36 AM
01/17/05 10:36 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Welcome to the forum, rusty. [Linked Image]

The most likely cause of the arcing is part of the neutral current is flowing through the GECs (probably the water line) back to the power company transformer.

This is normal and now that you tightened the screw you are all set.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,905
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,445 Are you busy
190,685 Re: Forum
180,402 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.042s Queries: 14 (0.003s) Memory: 0.9487 MB (Peak: 1.6133 MB) Zlib enabled. Server Time: 2019-04-19 09:08:45 UTC