I bought this on eBay. I had seen them in old catalogs, but never laid eyes on one. Use prohibited by NEC section 384-16 (e)beginning with the 1978 edition. The date on the box is May 27 1963, so it's almost as old as I am. NORCAL (edited to post clearer images) [This message has been edited by electure (edited 01-08-2005).]
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
The reason they were no longer permitted in Article 384 went something like this — They were used to provide one 3ø circuit in a 1ø 3w panelboard. The 1ø panelboard could serve a 3ø load such as a package air conditioner in a retail store where everything else on the feeder/service entrance was 1ø.
They were shot down as a potential shock hazard—where the 1ø panelboard disconnect was opened, there could be backfeed through the highleg in the ‘outboard’/'delta' 3ø circuit through the served 3ø load. Norcal’s pictured ‘4-space/3-pole’ breaker has 4 cable connections (lugs) and two bus clips to connect to two (1ø) ‘hot’ busses in the panelboard. The sole highleg breaker pole had ‘in and out’ cable lugs. It was a strangely fitting compliment to 4-wire delta electric service with an ‘outboard’ transformer for 240/120 4-wire (in some cases open-)delta systems.
[This message has been edited by Bjarney (edited 12-19-2004).]
|
|
|
|
Joined: Sep 2004
Posts: 167
Member
|
Wow even though there was a potential shock hazard, it was still marked "safetybreaker" on the box!!
Very educational
Larry LeVoir Inspector City of Irvine, CA
|
|
|
|
Joined: Sep 2002
Posts: 924 Likes: 1
Member
|
What is called the Cutler-Hammer "Classic" now had "Safetybreaker" on the package for many years.
|
|
|
|