How Far Will Electric Lines Arc? #150341 02/21/05 05:28 PM
Joined: Feb 2005
Posts: 2
J
Jim Patterson Offline OP
Junior Member
How far will OH lines carrying 7.2 kV arc? I have a technical reference that states it will arc 3/8" per kV, but an employee challenged my position, stating that distance could be increased by such factors as blowing dust, rain/snow, and magnesium chloride from DOT snow plows. We know the OSHA rule od 10 feet for lines of 50 kV, with multipliers for voltages above that, but I wish to know what your experience tells you.

Arc Flash PPE Clothing, LOTO & Insulated Tools
Re: How Far Will Electric Lines Arc? #150342 02/22/05 03:36 AM
Joined: Jul 2002
Posts: 8,337
Trumpy Offline
Member
Gidday there Jim,
Welcome to ECN, mate!. [Linked Image]
I work on Live 11kV-66kV lines as a course of my daily work, as a Line-Mechanic here in New Zealand.
Now, the flash-over distance is a function of the E-M fields that surround a conductor that carries a current, where an earthed (Grounded) part, enters that field.
With 11kV here, we are required to have a clear working distance from bare, live lines of at least one metre (3ft), until such time as the lines are sleeved and covers are in place.
That is working from an IEWP (Insulated Elevated Work Platform).
Full PPE is required even after the gear is in place.
Even then, most of our work is still done via Hot-Sticks.
The further you can keep yourself away from that sort of energy, the better.
It hath no friends once it escapes
Bjarney or Charlie, may be able to prove me wrong.
If they can, please guys, bring it on!. [Linked Image]

Re: How Far Will Electric Lines Arc? #150343 03/16/05 02:55 AM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
 
Aaak! Sorry for the month-late reply. Legally, US electric-power workers at that voltage are bound by table R6 minimum approach distance in 29CFR1910.269 (OSHA utility rules) at www.osha.gov which ranges about 2 ft. 1 in. to 3 ft. 6 in. for the voltages listed by the OP. For wind and rain, it can be MUCH more critcal. Most contaminants would intuitively seem to worsen the situation requiring greater clearances. For inorganic salts, you might as well swimming in a pool of mercury—that’s anybody’s guess; extremely dependent on concentration and best avoided if at all possible.




[This message has been edited by Bjarney (edited 03-16-2005).]

Re: How Far Will Electric Lines Arc? #150344 03/16/05 05:47 AM
Joined: Jul 2002
Posts: 8,337
Trumpy Offline
Member
YaY!!,
Welcome back Scott!. [Linked Image]
Nice to have you here.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,700 Are you busy
204,940 Re: Forum
193,051 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3