0 members (), 567 guests, and 9 robots.
#144956 02/11/06 04:16 PM
U
Good one Paul,
That's the lines I was thinking along.
Bearing in mind we are talking about a 240V coil, (one Phase -> Coil -> Neutral) not a 415V coil (L1 Phase -> Coil -> L2 Phase).
So when would a 240V coil be used instead of a 415V coil? As you already have 3Phases to use, & in some instances, if you use a 240v coil, you have to run a Neutral back to the Board anyway, as only 3Phases & Earth
are Supplied.
Would it something to do with safety, ie; less Voltage in wiring running to remote Switches, where operaters of the machine could be working?
All I Wanted Was A Cup Of Tea!!
#144957 02/12/06 07:36 AM
It would affect the switch rating. On a 415V coil wired phase-to-phase, when you hit the E-stop switch and open the contactor circuit there will be 415V across its contacts.
Using a 240V coil phase-to-neutral would allow a 250V rated switches to be used instead.
#144958 02/24/06 04:11 AM
Sorry Paul,
I see your point.
At this point in time there is a LOT of pressure on us PoCo workers here locally and some of us have had that for some months.
My apologies for upsetting this topic,
Mike. [Linked Image]
