#14318 09/19/02 07:32 AM
Joined: Mar 2002
Posts: 37
E
EVAD7 Offline OP
Member
WHERE DO YOU FIND A CODE REFERENCE TO A SINGLE CONDUCTOR IN A RACEWAY. CAN YOU RUN A NEUTRAL FROM A 240V 3 PH IN A PVC CONDUIT?

Horizontal Ad
#14319 09/19/02 07:55 AM
Joined: May 2001
Posts: 717
G
Member
Single conductors in a raceway are referenced in Chap. 9, Table 1. You will find it is very rarely legal, usually referencing a Grounding Electrode Conductor.

300-3(b) All conductors of a circuit, including the neutral SHALL be contained in the same raceway, trench, etc..

Without a very lengthy explanation, if the neutral is not in close proximity with the phase conductors, your fault levels become unmanageable. They must be very close to each other, unless DC, for the system to function through all it's parameters.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,685
Joined: October 2000
Top Posters(30 Days)
Popular Topics(Views)
333,639 Are you busy
259,012 Re: Forum
240,428 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5