tsolanto My intention was to say that the conduit on each side of the LB, or enclosure would need to be strapped within three feet. Guess I need to re-read my post to see if it make any sense, HUH.
Don — in your 8/10 posting about need for independent {other-than-raceway} support in the case of using reducing bushings, wouldn’t drilling bolt holes in most {all?} cases constitute modification of the conduit body? I am not aware of conduit bodies furnished with lugs or other mounting means.
Can you or another suggest possible resolution to this? [I understand and do not object to the requirement for additional support.] Thank you for your time. —bjarn
I take it to mean, like Warren pointed out, that the conduit itself must be supported within 3' of the condulet if the condulet is over-sized with reducers connecting the conduit.
Make sense?
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI