AE-Gifts, Affordable Everyday
0 members (), 346 guests, and 9 robots.
#13729 09/12/02 05:20 PM
Warren1 how do you strap an LB?
#13730 09/13/02 12:32 PM
Redsy Offline OP
I actually screwed an LB once, but I wasn't comfortable about it.
I'm thinking doing so would violate 110.3(B)
#13731 09/13/02 12:39 PM
tsolanto
My intention was to say that the conduit on each side of the LB, or enclosure would need to be strapped within three feet.
Guess I need to re-read my post to see if it make any sense, HUH.
#13732 09/13/02 01:49 PM
Redsy Offline OP
never mind
[This message has been edited by Redsy (edited 09-13-2002).]
#13733 09/13/02 03:48 PM
Don — in your 8/10 posting about need for independent {other-than-raceway} support in the case of using reducing bushings, wouldn’t drilling bolt holes in most {all?} cases constitute modification of the conduit body? I am not aware of conduit bodies furnished with lugs or other mounting means.
Can you or another suggest possible resolution to this? [I understand and do not object to the requirement for additional support.] Thank you for your time. —bjarn
#13734 09/13/02 08:29 PM
I take it to mean, like Warren pointed out, that the conduit itself must be supported within 3' of the condulet if the condulet is over-sized with reducers connecting the conduit.
Make sense?
-Virgil
5 Star Inspections
Member IAEI