Please could Old Appy or anyone else who wants to have input, please tell me if an out-building that is 25 metres from the supplying Switch-board, run in Neutral-screened 6mm2, 3core, do I need to have a driven Earth Stake, or can I make this a Distribution board and take out the N-E link?.
Thanks Craig, Came in too late with this job, the cable had already been laid(not sure how deep!), Meggered it and got 150Megohms between the NS and all phases.(@1000V) Will drive a stake. Ever bent a stake in stony soil?, done it for the first time, last week, out at the local abbattiors, installing a 600A sub-main, the stake started to come up through the ground about 3 foot away from where I was driving it.