#130785 02/05/07 02:07 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
How close is KVA to wattage when reading on a transformer or machine, etc.


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#130786 02/05/07 02:10 PM
Joined: Mar 2005
Posts: 1,213
S
Member
It depends on the power factor, which depends on the load. Generally speaking, PF is between 0.8 and 1 which means kW is 80-100% kVA. But this isn't always the case; you may be able to calculate it based on nameplate data, but it ultimately will require a measurement to know for sure.

#130787 02/05/07 02:26 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
So the PF would be different according to the load and/or if its a 120/208 or 277/480v.
if that makes sense


The Golden Rule - "The man with the gold makes the rule"
#130788 02/05/07 10:48 PM
Joined: Sep 2005
Posts: 202
W
WFO Offline
Member
The voltage would not determine the power factor.

#130789 02/05/07 11:05 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
This is for a 400 volt machine 3 ph 63 amp.


The Golden Rule - "The man with the gold makes the rule"
#130790 02/06/07 02:05 AM
Joined: Aug 2006
Posts: 21
S
Member
It might help to review the power triangle to see the relationship of Real Power(P), Apparent Power(kVA) and Imaginary Power(kVAR).

The angle opposite the Imaginary Power side is known as the angle of phase offset, of which its cosine is power factor.

#130791 02/07/07 05:32 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Here is a simple example of the Power Triangle, which will assist with the Power Factor conclusion:
(it also doubles as the Basic Impedance Triangle, and the Basic Pythagoris Theorym)

============================================

4 Watts (True Power),
3 VARs (Reactive Power),
5 VAs (Apparent Power).

============================================

Power Factor = 0.8 (80%) lagging
4 Watts is 80% of 5 VA.
---------------------------------------------

Some detail to these items:

*** WATTS ***
Watts = True Power,
KW = Kilo Watts = 1,000 Watts;

*** VA ***
VA = Volt-Amps = Apparent Power = Reactive Power and True Power compiled,
KVA = Kilo Volt-Amps = 1,000 Volt-Amps = 1,000 VA;

*** VAR ***
VAR = Volt-Amps Reactive = Reactive Power = Scuttle Power,
KVAR = Kilo Volt-Amps Reactive = 1,000 Volt-Amps Reactive = 1,000 VAR.

In the example values listed above, the preceeding relate to listed Trigonomic Terms:

<OL TYPE=A>


[*] 4 Watts = "Sine" (Base of the Triangle),


[*] 3 VARs = "Cosine" (Opposite side of Triangle),


[*] 5 VAs = "Tangent" (Hypotenuse)
</OL>

You can use this formula to find any single unknown value, as long as you have two known values.

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#130792 02/11/07 11:24 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Bump....

Any update on this?
(Did the examples make sense + help?)

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#130793 02/12/07 07:40 AM
Joined: Jul 2004
Posts: 787
L
Member
Scuttle Power?

Is that supposed to mean the "power" that is scuttling back and forth between the load and the source, that doesn't do any real work, but requires us to upsize conductors and such, in order to accommodate its journey?

Larry C

#130794 02/12/07 01:07 PM
Joined: Sep 2003
Posts: 650
W
Member
I've never heard the term 'scuttle power', but seeing as how it is used as a synonym for reactive power, then 'power going back and forth between source and load' is exactly how I read it.

If you look at a sinusoidal load with a power factor less than 1, you will find that the sine wave representing current is not in phase with the sine wave representing voltage. This means that there will be portions of the AC cycle in which current has one polarity, and voltage the other, meaning that the load is supplying power back to the source. Over the entire AC cycle, the net power delivery is from source to load, but over part of the cycle there is a reverse flow of power.

-Jon