Max current load #130742
12/01/06 09:46 AM
12/01/06 09:46 AM
J
JakeJ1  Offline OP
Junior Member
Joined: Mar 2005
Posts: 3
charleston SC USA
Not necessarily an NEC/code question. If I have two 10Awg circuits using 10/3 with ground MC cable and I put these together in parallel, what is the max current load that this will support?

Tools for Electricians:
Re: Max current load #130743
12/01/06 11:13 AM
12/01/06 11:13 AM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 303
Ogden, Utah, USA
Article 310.4 discusses conductors in parallel. Using the information there we find that paralleling #10 is only allowed in limited circumstances and based on Exception 1 (b) we find that parallel #10 (referring to table 310.16) carry 30 amps at 60 degree C (no increase in ampacity).

Re: Max current load #130744
12/01/06 12:25 PM
12/01/06 12:25 PM
J
JakeJ1  Offline OP
Junior Member
Joined: Mar 2005
Posts: 3
charleston SC USA
Thanks for the prompt reply. I find it interesting that the overall ampacity will not increase when two like cables are placed in parallel.


Thanks again..

Re: Max current load #130745
12/01/06 05:34 PM
12/01/06 05:34 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
That is not always the case.

2 cables with 1/0 or larger conductors will have double the ampacity. 3 cables with 1/0 or larger will have triple the ampacity.

In general there is little benefit from paralleling conductors smaller than 1/0 and you can only do it for specific installations.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 9
Popular Topics(Views)
249,430 Are you busy
187,352 Re: Forum
176,691 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 14 (0.004s) Memory: 0.9588 MB (Peak: 1.0900 MB) Zlib enabled. Server Time: 2018-09-24 16:07:32 UTC