operation of 225kVA static UPS - ISSUES WITH HARMONICS #130422
04/13/06 07:35 AM
04/13/06 07:35 AM
V
vmac100  Offline OP
Junior Member
Joined: Oct 2004
Posts: 4
Dear All,
please, we have an electrical power supply installation to one unit of Balanced Power Plus 225kVA static UPS machine and two 75kW pumps. All three equipment are supplied power from the same busbar. We propose to install dual soft start panel to replace the existing dual star-delta panel that is presently used to power the pumps from the 415V LV busbar. The pumps are 3-phase.

However, we will like to know if we are going to be experiencing problems with harmonics when the pumps are running after we have installed the soft-start panel. We wish to know if this panel upgrade will cause an increase in the Total Harmonic Distortion (in current and voltage) and what the effect on the UPS will be. Also, we will like to know if there are equipment that we can install that will limit the THD to acceptable values (for the UPS) when the pumps are running.

Do treat as urgent and thanking you for your co-operation and support.

Tools for Electricians:
Re: operation of 225kVA static UPS - ISSUES WITH HARMONICS #130423
04/15/06 10:25 PM
04/15/06 10:25 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA

Re: operation of 225kVA static UPS - ISSUES WITH HARMONICS #130424
04/27/06 11:37 PM
04/27/06 11:37 PM
E
Erloq  Offline
Junior Member
Joined: Oct 2005
Posts: 6
Concord,CA,USA
Quick question...
A 225kVa UPS is a double conversion device and rather immune to terrible input power. Are you concerned about THD PoCo penalties?
Other than a active injection filter, voltage and current distortion will vary too much at startup and full load to be resolved by a static or tunned filter. Personally I wouldn't worry much about the UPS.
The UPS has already been exposed to mild/moderate surge and transients with the wye/delta starters. The EFI MOV's are typically the weakest link on the input of most UPS's.


Eric

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
richard
richard
L.I. New York
Posts: 98
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,208 Are you busy
189,191 Re: Forum
178,872 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.006s) Memory: 0.9523 MB (Peak: 1.0755 MB) Zlib enabled. Server Time: 2018-12-15 09:34:20 UTC