ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 8
Recent Posts
OD of Alum and Copper
by HotLine1. 08/23/17 07:30 PM
Grid problem??
by annemarie1. 08/21/17 01:10 PM
Bathroom electrical
by doc. 08/19/17 06:53 AM
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,162 Are you busy
175,811 Re: Forum
167,968 Need opinion
Who's Online Now
0 registered members (), 67 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#130384 - 03/20/06 06:34 PM Load Calculations  
rhpope  Offline
Member
Joined: Feb 2006
Posts: 18
North Carolina
When calculating the load for a building, how do you spread the single and three phase loads over the incoming three phase lines? I belive the correct way for 120/208 Wye is that single phase 208 or 240 loads spread equally across two transformers (A&B, B&C, or C&A) whereas for 120/240 Delta, 208 or 240 single phase load is applied to only one transformer (A, B, or C)/phase (just as the 120 loads are only on the A & C phases). The three phase loads are spread equally across all three phases.


Tools for Electricians:

#130385 - 03/20/06 09:18 PM Re: Load Calculations  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
You seem to have it correct. The only thing that's really tricky is that, on a delta with a high leg (B phase), any load that has a neutral connection, i.e., 240/120 or just 120, must be connected only to the other two phases (A or C), as you noted.

Typically, the high-leg delta system has less load on B phase than the other two, because only line-to-line or 3-phase loads are served by this phase, whereas A nd C phases serve all of the line-to-neutral loads.


Larry Fine
Fine Electric Co.
fineelectricco.com

#130386 - 03/20/06 10:39 PM Re: Load Calculations  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
I agree with your thinking about spreading the loads as equally as you can, which would be balancing of the transformer.

Using a 208/120Y transformer you can use any of the phases for 120V loads, any 2 of the phases for single phase 208V loads and all three for 3 phase 208V loads. However you can't use any combination of these for 240V loads...

Using a 240/120 Ct transformer, you can use A or C phase for 120V loads, any 2 phases for single phase 240V loads, and all 3 for 3 phase 240V loads. You can't use any combination for 208V loads....

Mind you with this type setup and using the high leg, you must be concerned about using full voltage breakers where with the 208/120Y setup, the use of "slash" breakers could be used.


Dnk...



[This message has been edited by Dnkldorf (edited 03-20-2006).]



Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7523 MB (Peak: 0.8796 MB) Zlib enabled. Server Time: 2017-08-24 06:55:49 UTC