motor disconnect question #129516
04/05/05 07:28 PM
04/05/05 07:28 PM
K
knopp  Offline OP
Junior Member
Joined: Jun 2004
Posts: 2
richmond, va
i have two 480 3 phase motors, the first is a 10HP (14FLA)and the second is a 30HP (40FLA) these two are to be fed from individual circuit breakers at a main lug panel and a fusible disconnect supplies the incoming power. how do you properly calculate for the correct size time delay fuses at the disconnect.

Tools for Electricians:
Re: motor disconnect question #129517
04/05/05 09:29 PM
04/05/05 09:29 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
How about 430.63, which would, in your case put you at 430.62?
40A x 175% = 70A
70A + 14A = 84A
84A + the lighting and appliance load on the panel = Time Delay Fuse size?

[This message has been edited by Redsy (edited 04-05-2005).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,459 Are you busy
190,701 Re: Forum
180,413 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9418 MB (Peak: 1.0594 MB) Zlib enabled. Server Time: 2019-04-20 06:30:33 UTC