3 phase current calculations #129346
01/25/05 06:49 PM
01/25/05 06:49 PM
D
DJT  Offline OP
Junior Member
Joined: Jan 2005
Posts: 2
Indianapolis, In. 46221
I AM PROVIDING TRAINING FOR OUR PLANT ELECTRICIANS, AND I WANT TO CONFIRM A COUPLE BITS OF POWER THEORY PRIOR TO GOING LIVE.

EXAMPLE: 13,800V DELTA, 480-277V WYE, 2000KVA
TRANSFORMER.
X1 HAS 1000 AMPS
X2 HAS 1200 AMPS
X3 HAS 1400 AMPS

I HAVE ASKED THEM TO CALCULATE:
NEUTRAL CURRENT
ALL 3 DELTA LINE CURRENTS
ALL 3 DELTA PHASE CURRENTS

TO SOLVE FOR NEUTRAL CURRENT;
THE SQUARE ROOT OF...
1000 SQUARED + 1200 SQUARED + 1400 SQUARED
= 2098 AMPS
DELTA PHASE A CURRENT = 1000A/49.819 = 20AMPS
............B CURRENT = 1200A/49.819 = 24AMPS
............C CURRENT = 1400A/49.819 = 28AMPS
49.819 IS 13800/277.
DELTA A LINE CURRENT = 20 X 1.732 = 35AMP
......B LINE CURRENT = 24 X 1.732 = 42AMP
......C LINE CURRENT = 28 X 1.732 = 48AMP

I REALIZE THAT WITH THESE IMBALANCES, THERE WILL BE PHASE SHIFTS, BUT 120 DEGREE ANGLES WERE USED TO SIMPLIFY.
I HAVE A 50/50 CONFIDENCE LEVEL WITH MY CALCULATIONS.

Tools for Electricians:
Re: 3 phase current calculations #129347
01/25/05 08:28 PM
01/25/05 08:28 PM
C
crash  Offline
Member
Joined: Oct 2003
Posts: 147
Calgary Canada
I got 346.4A for the neutral current. The other figures seem to be correct.

The neutral current is calculated by adding the line currents in a vectoral manor.

[This message has been edited by crash (edited 01-25-2005).]

Re: 3 phase current calculations #129348
01/25/05 10:34 PM
01/25/05 10:34 PM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
The Delta line currents are the vector sum of the phase currents at each node, so you can't simply multiply the phase currents by root three. Even if you are making the simplifying assumption of 120 degrees between each phase, I get 38.16A, 41.62A, 45.08A...I've not double checked this.

-Jon

Re: 3 phase current calculations #129349
01/26/05 09:21 AM
01/26/05 09:21 AM
C
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
Try this it' always worked for me.

I N =Sq root of A2 + B2 + C2 – A.B-B.C-C.A

Essentially this provides the vector sum of the three currents. It works if one phase is not utilized also.

Re: 3 phase current calculations #129350
01/28/05 08:39 PM
01/28/05 08:39 PM
S
scameron81  Offline
Member
Joined: Feb 2004
Posts: 75
Healdsburg, ca, USA
Here is a great explanation of the nuetral currents on wye systems. It even has the formula to calculate the netrual current.
http://www.electrician.com/electa1/electa3htm.htm


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Khombo 2
Popular Topics(Views)
255,847 Are you busy
191,824 Re: Forum
181,600 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9682 MB (Peak: 1.1061 MB) Zlib enabled. Server Time: 2019-06-25 03:44:52 UTC