ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

Nightmare Panels
Nightmare Panels

Random Gallery Image:
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 67 guests, and 26 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jan 2005
Posts: 6
S
Junior Member
hello there. the electrical utility that serves our place supplies a secondary of 240/208v 3ph,4 wire Delta.will it be ok if a 4 wire, y motor be supplied by this? is it safe if i put the common wire of the motor on the ground wire of the delta supply? What would happen if i do this?

thanks again.....


Oh Yeah!
Horizontal Ad
Joined: Aug 2001
Posts: 7,520
P
Member
Is the motor designed for a wye connection to 120/208 volts?

You won't be able to connect directly to the 4-wire delta (the high leg will be 208V to neutral, and the phase angles will be wrong anyway).

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The utility supply voltage is probably 240/120 3 phase 4 wire delta.

The internal construction (winding arragnement) of a motor is not a factor. all you need to worry about is what external connections (leads) are provided.

If you only have 3 voltage leads (one per phase) then your motor will work fine. If you need 4 wires to your motor (extremely rare) it will not work on your 4 wire delta service.


Link Copied to Clipboard