Scott,
If there is a high starting torque required, wouldn't the use of wye/delta starting increase the likelyhood of the motor stalling?
Don
#129298 01/14/05 09:38 PM
This thread's subject is definitely worthy of some Schematics!
I'll cook up some with low and hi volts arrangements.
Being that the Nameplate of this Motor shows 200/400 VAC, the Delta Run config with low voltage jumper terminations on the 208 VAC System should be OK.
Don,
I was thinking lower speed/torque starting application to get things moving (things being some fluid and the Motor's Rotor), then applying Motor across the Line after a few seconds.
Along with this, there may be some problem with high enough System Voltage at the time of starting (things faulting out from the fire, just flat-out lower than normal Line Voltage at the time of starting, etc...), which is another reason why I chose to go down this particular thought path.
Like I said, most likely not correct, but worth a thought!
Seems the flicker factor of starting this Motor is overridden by the need to get the Fire put out
(or: Sorry for the lights dimming people, we have more important issues to address - one being these frikken flames are growing in intensity!!! Scenario).
Could you explain the benifits of a Reduced voltage (Wye/Delta) Starter for the 20 HP Fire Pump?
I'm at a loss, except for the reason previously mentioned; so if anyone has the definite reasoning, please pass it on!
Scott35
#129299 01/15/05 01:08 AM
Scott,
Maybe that was the only way to comply with 695.7.
Don
#129300 01/15/05 05:18 PM
That's a funny; prevent a 15% voltage drop by intentionally applying 42% voltage drop [Linked Image]
-Jon