To effectively damp phase-to-ground overvoltage in an ungrounded system (with complete equipment grounding and bonding in place) the capacitance between phases and ground must be damped by a resistor connected from neutral-to-ground.
“Charging current” for 480V systems is roughly 1 Ampere/1,000kVA of system capacity. [In the case of delta systems, the neutral has to be derived from zig-zag or wye-primary—delta-secondary transformers.]