wendel Offline OP
Member
I have a blower motor for a furnace. It's a 3 speed, PSC, 1/4hp, 1050rpm, 115 volt generic HVAC motor. My problem is that even at the lowest speed, the blower is moving too much air.

Is there any way to slow the rpms of this motor down further below it's lowest speed setting?

Joined: Dec 2001
Posts: 300
M
Member
You could change the blower (supply house will size one for you) or add a damper.

Joined: Oct 2000
Posts: 2,722
Broom Pusher and
Member
Could reduce speed via belt/pulley arrangement, or insert an Autotransformer in series with the Line Input of the PSC Motor - as this is the common method of speed reduction on the PSC fan Motors (Autotransformer wound into the Stator of the Motor).

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 70
Joined: January 2002
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,066 Are you busy
233,475 Re: Forum
218,159 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5