ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Jan 2004
Posts: 105
C
Member
Hi- the flame circuit needs to read a ground path through the flame-which is flame rectification. this is a mA circuit that, when not present whether because of a poor ground or a dirty sensor, will present itself exactly as you describe-3 tries and a lockout. this sensor usually resembles a spark igniter electrode and is at the opposite end of the burner assy. from the igniter. While the unit is on the grid, you could disconnect this sensor and see the same behavior. That being said, there must be something about the gen-sine. Perhaps a small ups/conditioner would do upstream from the control board, so it wouldn't need to be sized for the fan motor. Have you checked the frequency of genset output?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 2,527
B
Moderator
"High speed" {sub-cycle} voltage changes cannot reliably be measured with a voltmeter. That's what oscilloscopes and related power-quality instruments [and consequent bird-dogging] are for.

Joined: May 2004
Posts: 7
F
New Member
I suspect that a ferroresonant transformer will have a faster response time than a furnace and should resolve the problem. The advantage over a UPS is that the transformer doesn't need the maintenance of that a battery requires.

<< A ferroresonant transformer, also called a constant voltage transformer, will give a constant AC voltage output when the input voltage varies within the rated input voltage range. Typical response for output regulation is plus or minus 3% for input voltage swings that are within the rating of the transformer. Typical response times are 8 millseconds for a 5% line or load variation, and 16 milliseconds for a 10% variation. Generated harmonic distortion will be less than 3%. >>
http://www.powerqualityanddrives.com/sag_correction_without_ups/