C
Junior Member
I installed a Gentran swith in a house the other day and I checked out the generator (Generac 4000w), when I checked it I found the voltage from the hot leg to ground was 0 zip nada.... I tried to call Generac, and got a local sales rep who knew jack about it. I had a similar problem with a Honda generator (hot to ground was 65volts) and when I called them they said that was normal for that model.
Ok, so when these generator's are being used as a back up power source in a dwelling doesn't it become a seperatly derived system? And shouldn't the neutral be bonded to the ground in the generator?
I would appreciate anybodys input. Thanks in advance.

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
The generator only becomes a separately derived system if the transfer switch transfers the neutral (breaks the neutral). If that is the case then you must connect the neutral to the frame of the generator with the bonding strap. You will also need to install a grounding electrode. If the neutral is not transfered then the bonding strap must be removed and the neutral conductor is connected to the neutral terminal on the generator. The green grounding conductor from the house wiring is connected to the frame of the motor. In your case where you did not get a reading from the hot leg to ground may have been because the ground strap was not in place. I hope you got a reading from hotleg to neutral.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Top Posters(30 Days)
triple 2
BigB 1
Popular Topics(Views)
304,938 Are you busy
233,352 Re: Forum
218,073 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5