Load calculations for SDP #127796
01/03/02 02:34 PM
01/03/02 02:34 PM
A
ayrton  Offline OP
Member
Joined: Dec 2001
Posts: 201
Pa
I need to calculate loads to install a distribution panel fed from a transfer switch.
I have a 200a,
175a
150a
125a breakers all three phase.
None of which the branch circuits draw anywhere near the breaker size. Ineed to put these breakers with their circuits into one panel to be fed from a tranfer switch which of course will be rated accordingly. I know I just don't add these up.

Tools for Electricians:
Re: Load calculations for SDP #127797
01/03/02 09:49 PM
01/03/02 09:49 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
What are the actual loads?

Re: Load calculations for SDP #127798
02/06/02 12:47 PM
02/06/02 12:47 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
The size of the breakers does not provide you with the needed information. You need connected load, name plate data from the equipment connected, clip on amp readings on each phase and any other info you can get.
After accumulation of the information you can make a decicion as to what size equipment you will need. Add 25% for future load. Its possible that the old load has been removed and the present breakers size
is not required

[This message has been edited by Bob (edited 02-06-2002).]

Re: Load calculations for SDP #127799
02/06/02 11:36 PM
02/06/02 11:36 PM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
As suggested, you will need to compile Panel Schedule[s] and do a Load Calc [like the NEC Service Feeder load calc].

If you need answers to these items, feel free to post again - leave no details unposted [Linked Image]

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Albert 2
Popular Topics(Views)
251,513 Are you busy
188,688 Re: Forum
178,390 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9602 MB (Peak: 1.0942 MB) Zlib enabled. Server Time: 2018-11-16 18:05:42 UTC