#123856 06/02/06 07:46 AM
Joined: Dec 2000
Posts: 4,294
Member
Dnk,
The biosolids, or sludge, from the sewage treatment plant just down the way from the water replenishment facility is trucked out and composted...230,000 tons of it a year.
Currently, the wastewater is all sent out a pipe 4.5 miles offshore and discharged in about 200' of water. Many believe that it's the source of bacteria that often forces beach closures. The new plant will take a load off of this discharge....until population growth catches up with the whole thing again.

Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

#123857 06/02/06 11:09 AM
Joined: Apr 2004
Posts: 55
B
Member
Celtic,
The terminations aren't bad. You just think of it as a splice, and put a terminal lug on it instead of a butt.

We have 4 2500 HP motors here. It is impressive when they start up. (across the line).

#123858 06/02/06 05:23 PM
Joined: Feb 2005
Posts: 361
C
Member
Here's a question...where's the peckerhead? (junction box for the motor and line terminations/connections for anyone before they have to ask )


~~ CELTIC ~~
...-= NJ =-...
#123859 06/02/06 06:59 PM
Joined: Oct 2004
Posts: 806
Member
Celtic, I think the terminations for the motor itself are in the large rectangular can with the number on it, near the top of the motor.

Big Ed, impressive in what way? I would imagine the noises both the motor and switchgear make to be interesting and a bit scary.


Stupid should be painful.
#123860 06/02/06 07:21 PM
Joined: Aug 2001
Posts: 599
N
Member
Yes, the large box is the peckerhead. Inside is bus with the standard NEMA 2 hole pattern so in this case it's just a standard MV termination. We are going to have to turn them 90 degrees because they are getting fed via cable tray that will run along side just to the right of the beam you can see. There are 3 tiers, 4160, 480 and controls. Like I said before the small box you can see is the heater termination box and there is another box on the other side, out of site, where the inlet/outlet temp, bearing temp and vibration RTD's terminate into a terminal strip.
Electure, interesting tid bit of info. The water from this plant will come from OCSD plant 1 next door via a 96" pipe. It has already been treated but is still pretty stinky. The finished product will be split between being pumped into the ground water and pumped all the way up the Kramer basin near the 91/55 junction where it will settle naturally into the ground. They have had the Santa Ana river trail closed for some time installing that line.

#123861 06/03/06 10:11 AM
Joined: Aug 2004
Posts: 42
H
Member
Nick,
Are you using shielded cable on this?

HP

#123862 06/03/06 12:08 PM
Joined: Feb 2002
Posts: 840
C
Member
This looks like a very inexpensive project. [Linked Image]

Peter


Peter
Software for Electricians

Software for Electricians, Installers & Maintenance Technicians

#123863 06/03/06 12:20 PM
Joined: Aug 2001
Posts: 599
N
Member
Yes, the VFD manufacturer requires 8KV shielded or non shielded cable. We are using shielded per project specifications. It looks like we will go with 3M QT-III terminations. Believe it or not this project is still under the 96 NEC so if it wasn't for the spec non shielded would be an option.

Cable

#123864 06/04/06 12:44 AM
Joined: Aug 2004
Posts: 42
H
Member
Reason why I asked, it looks like it might be tough to make the terminations in that small an area. Non- Shielded would be a breeze.

HP

#123865 06/07/06 07:53 AM
Joined: Apr 2004
Posts: 55
B
Member
mxslick,
The noise and the voltage dip.

They are the feedwater pumps at a power plant. 2500 psi output. It looks like an old prison movie when they start. All of the lights dim for just a second.